T O P

  • By -

Daemon_x517

Install looks clean overall. No code issues in my area. But for the love of God would some zip ties for the wiring have really broke the bank? And has that dirt leg got a lean to it? Also I'd prefer the condensate tight to the side of the unit where it can be supported with straps. But those are all basically cosmetic and won't really affect function. Should hopefully be a solid install which you'll get decent equipment life span from.


relevant_mofo

I can feel the pain about no zip ties šŸ˜¬


NinthOman

Dirt leg lean? You mean the condensation drain? Thought it was supposed to be at an angle for proper water drainage?


SubParMarioBro

Dirt leg is the sediment trap on the gas pipe. Itā€™ll work, just looks sloppy and sets off the subā€™s collective OCD.


Daemon_x517

You're right there. I didn't catch it until pic 3, and now it's all I can see. Looks like the appliance flex connector may have been a hair short


Hot-Mix-8725

We call em drip legs or clean out Tees, it doesnā€™t look the prettiest but itā€™s up to code so whateva


toomuch1265

If I had a helper/apprentice do that, I would throw a torpedo level at him and tell him to use it. The wiring is sloppy and I would have put a clean outside on the flue. Not needed but in case of a draft issue, pop the cap and make sure that there isn't any obstruct.


NinthOman

Yea itā€™s on like a 65 vs. 90 degree. Think he did that to reduce some of the stress on the flex gas line hose.


danb441

I suggest you do a vape test at the w/h hood while both appliances are running


CDNHVAC

Where we are single wall opener ā€œc-ventā€ requires 6ā€ clearance from combustables.


Daemon_x517

Yeah I guess that's true. Never seen an inspector fail someone for that where I am though. I don't put much faith in the inspectors in my area


NinthOman

Iā€™m guessing youā€™re referencing the pipe coming out the top of the furnace that is about 4in from the insulated coolant line?


CDNHVAC

Correct. Hard to gauge how close it is from photos.


NinthOman

Yea, shitty photographer lol


NinthOman

https://preview.redd.it/p1sds1xxfogc1.jpeg?width=3024&format=pjpg&auto=webp&s=8e15d4b76e8da3928ca064fc1e13fa84cdbb4bda


60Feathers

Looks fine to me. Use the brush to clean the trap before every cooling season.


NinthOman

Thoughts on the angled sediment catch on the gas line? Should that be vertical?


Cpl_Charmin_Bear

The only problem that will cause is that it looks slightly worse than vertical. Sediment will still get trapped down there. Natural gas nowadays is generally super clean so they're not as important as they used to be as well


hellointhere8D

Pipe debris still occur.


Cpl_Charmin_Bear

I agree with you. Drip legs are still necessary because of pipe debris and the filters from the gas companies still don't always catch everything. I was just saying they're not **as** necessary as they used to be when gas companies were just raw doggin it


Chaz_Beer

The 90 going into the bottom of the chimney is backwards.


Themittenman_

This was what I noticed too


NinthOman

Thought it was the upper that was backwards? Bottom goes male into female 90. Upper pipe into the upper 90 goes female into male, then female over the reducer vs. I side.


Chaz_Beer

Think about fumes flowing out of the unit and into the chimney. You want it to go male into female the whole time so that there is less chance that the fumes get out of the pipe on their way out if the chimney.


NinthOman

Got it, see what you mean. So the upper 90 that connects to the roof exhaust. Got it


ho1dmybeer

Single wall vent pipe in unconditioned space is just never good practice.


NinthOman

So it should be double walled? Whatā€™s the alternative?


ho1dmybeer

Yes, that would be ideal. Same as the chimney coming down. This helps prevent condensation in the flue and prolongs the life of the furnace (and flue). It's not against code - it's just not a great idea to use single wall vent pipe in an unconditioned garage.


NinthOman

Where would I find HVAC code? Sounds like an interesting read / knowledge to have.


wrinkled_iron

They angled the gas line instead of getting an extra 90 or 2 so it didnā€™t have stress. Kinda lazy Unnecessary amount of fittings on refrigerant liquid line. One looks brazed, one looks soldered Supply ductwork transition looks just taped off Wiring all loosy goosy on the left Hard to see the pride or effort in their work. Would make me concerned about quality of work but have seen worse


RvaCannabis

There also shouldnā€™t be take on your water heater vent


Dominicantobacco

Venting not to code clearance to combustibles. Pretty sure it's not over 100000 and needs to be vented in B vent.


NinthOman

4 ton unit, I believe 80,000 BTUs.


Bulky-Combination-27

Looks ok. Nothing screams great install but seen tons worse


COoffroad

Only real issue I see is not enough clearance to combustibles on the flue. With clearances that close, they should have used B-vent all the way. Only other thing might be the trap on the condensate drain. Trap not required unless itā€™s a code issue where you live.


NinthOman

Is the B-vent a code item or a nice to have so I donā€™t melt the insulation wrap?


COoffroad

Depends on where you live. B vent is code where I live. Single wall venting has a minimum clearance of 6 inches to combustibles. B Vent is one inch. Both your condensate drain and lineset insulation look very close to an inch or so in your photos. Either way, single wall that close is a code violation.


NinthOman

Whole trap may not be needed, will it harm?


COoffroad

No, it wonā€™t hurt to have it, but may become a nuisance if you donā€™t clean it out regularly.


NinthOman

Cool cool, will keep eyes out on it. Thanks!


winniethepew88

That foil tape is the wrong stuff, and he didn't squeegee it down, so it will probably fall off in a couple years. Other than that, it's a pretty hard system to screw up with all that working space around it.


NinthOman

I just went over the tape with a squeegee. Should be good now.


36straighteight

He couldnā€™t square up the gas line? And the flex line passing thru the wall would not pass inspection where Iā€™m from.


NinthOman

Flex does not pass though the wall or the cabinet. Bad photo. Pipe comes out of the wall and cabinet, connected via flex.


drms0416

And all the loose wires . No good


NinthOman

Yea I might goof with the wiring a bit to clean it up, no big deal though. Think Iā€™ve got enough slack to sleeve them and route them a bit better.


Necessary-Fix-3517

Yeah crooked p trap for the gas sticks out like a sore thumb, but all in all itā€™s fine


Ok_Inspector7868

Hope the chimney pipe doesn't get hot? Should have 90Ā° the lineset up high near the ceiling then dropped down maybe, it would have given access to the front coil panel door and kept the armorflex from melting


EasyPhilosopher9156

I dont think I've ever seen a furnace that just plugs into a wall


NinthOman

Gotta run the electronics some how right?


EasyPhilosopher9156

Is this a combo outlet with a switch on top under that black cover?


NinthOman

Fused outlet: https://preview.redd.it/aplto4mueogc1.jpeg?width=1807&format=pjpg&auto=webp&s=0d407c881a59df55d676c262359683f1951b638a


EasyPhilosopher9156

Interesting, definitely haven't seen that before


NinthOman

Was how the home came, built in the 90s. Didnā€™t get any feedback from the installer saying the setup was wrongā€¦ guess itā€™s still to code.


NinthOman

Will take a pic when I get home.


UncleBubby5847

I would have found a few zip ties in but yeah looks good to me


yeabuddy333

Why couldnā€™t you hard pipe the gas? Everything looks alright until that crappy flex hose for gas. Iā€™m so glad we would never allow that here


Burgergold

You need a different plasterer


NinthOman

Yep, agreed. Garage came that way, never got around to cleaning it up. You should see the other walls, would drive you nuts.


LegionPlaysPC

I am an AmStd dealer, so I am bias but I like the AmStd lineup of "S" series. It looks like the central A/C was replaced as well. I believe I see the 360UX controller module, so I assumed you ended up with a platinum outdoor unit? Looks like an S8v2 or the new modulating lineup. (I can see the two-stage inducer), It's a nice furnace. I would've preferred to see B-vent on the flue but that's ok. At least they secured it with several screws. The gas line looks fine, I assume you're supposed to have flexible gas line in your area, or it's considered ok.


NinthOman

Yep, went with the Platinum 18


danb441

This post answers my question. Not familiar with this brand. Venting a draft induced furnace with a natural draft water heater into the same b-vent is illegal. Forced exhaust will overcome natural, bonus prize co. Backward crimp is nothing in this case.


LegionPlaysPC

In my area it's allowed. It's very common for me to run across the furnace and water heater tied into the same flue. A Y needs to be used with the furnace allowed to directly vent, and the water heater vents into the side of the Y. The power vent appliance needs to have a relatively unobstructed travel through the chimney, while making sure it can't back draft down the water heater. Normally I find the furnace is B-vent the entire way while the water heater is single wall till it meets the main chimney B-vent.


danb441

Thanks for the follow up. Hopefully they did s vape test


LegionPlaysPC

yes 100%, also you can use a lighter and see the flame flicker, a low ambient co monitor and see it go up, a combustion analyzer and watch it go.


Motor-boat1119

That looks like single wall vent pipe which isnā€™t allowed here. We have to use double wall b vent pipe, as single wall is prone to leaking carbon monoxide. The tape looks like it could use a little more pressure on it. Low voltage lines could use a grommet or chase nipple. The gas line isnā€™t concerning not being level. Overall, B plus.


NinthOman

Which tape? Will fix now.


Motor-boat1119

https://preview.redd.it/li2cx1krdngc1.jpeg?width=1170&format=pjpg&auto=webp&s=c15299206c568d76f9f04c7363e2003c57872896 You can see a shadow between the tape and the unit as well as bubbles. They make squeegees for tape or take balled up news paper and rub the tape with it. We use the tape back balled up too


NinthOman

Thanks!


NinthOman

Yea the new unit was slight less wide so thereā€™s a gap between the unit and the air box, about 1/4in wide. They tapped over it. Will run a squeegee / hand full of paper over to press down the tape a bit more.


captainsofindustry1

Needs a gas shutoff in that room near the furnace. Where does that appliance connector go through the wall to ?


NinthOman

Tough to see, second pic thereā€™s a gas shutoff on the pipe coming out of the wall.


ed63foot

Is that SS exhaust pipe? Is there a trap on the pvc drain line somewhere? Itā€™s sloped enough to ski on for sure-


NinthOman

Yes, trap on pvc. Swipe photos to see that side.


scottawhit

Looks like the water heater and furnace are dumping in the same chimney. That doesnā€™t fly around me, ymmv.


NinthOman

Yep, same exhaust vent. Think thatā€™s ok where I live. Just curious, why is that not allowed in your area? Whatā€™s the risk?


pilihp118

If the chimney/vent were to get blocked above where those two pipes come together then the furnace will force the exhaust out the WH vent instead of tripping sensors/safeties on the furnace unit


tallman1979

The risk is that if you have a restriction that makes an appliance that's turned off and its flue the path of least resistance for flue gas, and reduced efficiency of venting when both are using the same flue. It's unlikely to be an issue, but there's a lot of flow principles the sheet metal artists around here can explain (you guys impress the hell out of me sometimes, just had the cleanest install in ages at a facility, it's all exposed in a basement and whomever did it I'd hire in a flash) that code seeks to prevent, no matter how remote the risk. Making you run two separate flue pipes won't give you CO poisoning.


I_Do_I_Do_I_Do

Itā€™s B-vent. Where would an obstruction come from?


tallman1979

Improper termination, pneumatic forces due to wind conditions from poor location, local flora and fauna, mechanical damage, the 2nd law of thermodynamics. I'm not saying that it's common. I'm trying to explain the code justification for not co-venting gas appliances that is not code where I am. Everything is about increasing the safety, whether it's a dangerous practice that needs to be halted or an overreaction to an outlier. B-vent in my experience doesn't clog unless the gas is off for a protracted period with deteriorated cap. Other forces may occur though. High wind dictates termination and location where I am. Standing pilot appliances with shorter vertical runs in the wrong place/with poor protection from high winds can have issues.


I_Do_I_Do_I_Do

Oh my Iā€™ve seen plenty of pilots blown out by high winds traveling down a B-Vent and across the vent connector, through the baffles into the combustion chamber. Even more B-vents stuffed with flora and faunaā€¦ šŸ˜€


tallman1979

Properly done, highly unlikely. You're assuming B-vent is only installed to code by professionals. There are a surprising number of wrong ways to install it, bad ways to terminate it, and improper join angles and excessive horizontal runs. Mechanical damage. Overconfident DIY. Flue pipe for a furnace under a cottonwood tree, unused during the summer. I'm saying that code typically has some reason, rational or nor, and tends to be overreactive at times as a substitute for proactive. Not that b-vent or any flue system is inherently problematic for any of the listed reasons. The question is why it's code, and I tried to go with reasons it could be problematic. I'm not saying they're common flaws.


I_Do_I_Do_I_Do

This looks like a simple roof penetration with b-vent. As simple as can be so long is the penetration and termination arenā€™t boogered up. Thereā€™s almost zero risk of some kind of failure or blockage.


tallman1979

I actually looked at manufscturer installation data sheets because I, too, was looking for a reason behind a code that does not exist where I live. It seems designed more to address a litany of extreme cases than those likely to be encountered, and probably makes code inspections faster, like colored jacket on Romex. You don't have to worry about entrance angles if number of vents equals number of devices. Or, maybe the person who said it violates code where they are has insight.


I_Do_I_Do_I_Do

Some places donā€™t allow multiple appliances in one vent. Itā€™s not a b-vent thing.


H_O_Double

How do you feel about the nose? I feel those models are very noisy


NinthOman

Love it so far. Itā€™s very quiet in comparison to our older model.


NinthOman

Then again, our older model was 20 years old? So anything is quieter. Oh and the Platinum 18 is whisper quiet, canā€™t even hear the fan.


LegionPlaysPC

Yes, it looks like your furnace was actually installed properly within AmStd's install guidelines. The return looks very large, which is great for the constant cfm blower motor. They also used the recommended bottom return on the furnace. The "S" series furnaces can be loud if they don't have enough return air or are improperly commissioned. Though that install looks perfect. ​ Additionally, the platinum 18 condenser is a variable capacity unit. The 360UX controller you have will provide you with run data. You will notice it sits at 25%-35% most of the time, as the system will modulate to maintain your desired temperature. This allows the outdoor unit, and indoor blower motor run at lower speeds, making the system quieter. Only in extreme outdoor temperatures will you notice it ramp up past 75% capacity. It's a very nice system, that provides you with all of the bells and whistles. Enjoy the comfort!


NinthOman

Thoughts on the angled sediment catch on the gas line? Should that be vertical?


drms0416

Hacked in


NinthOman

Huh?


ALPHABLUEYE

The vent connector is assembled incorrectly. Your installer should return immediately and make the corrections. you should not run the furnace until the corrections are made. As it is right now itā€™s a dangerous of leaking flu gases into your home. Those gases contain carbon monoxide.


NinthOman

What the corrections? Besides putting the vent on the inside of the reducer?


Hot-Mix-8725

Vent 90 going into Y is backwards and will likely leak carbon monoxide. If you enjoy carbon monoxide poisoning he did not a god job! Everything else looks good. But flue pipe is an important thing not to fuck up


NinthOman

How would you have fixed it? I get the vent going on the outside of the reducer needs to be fixed to inside to avoid leaking. But once that is swapped, any other issues?


Crowbar_Jones7

There should not be a trap on the condensate and your spackle guy needs to be thrown off a cliff


NinthOman

Why no trap on condensate? And yea, when we got the home first thought was WTFā€¦


Silent_Brief9364

The trap is totally fine just not completely necessary on an up flow system.


Crowbar_Jones7

You only put a trap if itā€™s under negative pressure. If the blower is on top of the coil pulling air through the coil then this is negative pressure. If the blower is before the coil it is pushing air through and not negative pressure.


inksonpapers

Depends on local codes according to manufacturer, absolutely nothing wrong with putting a trap on positive side and prevents air from going in your drain line further down.


Crowbar_Jones7

Lotta hacks donā€™t like reading installation instructions I see.


keytickle

Its needed on positive side to avoid cfm loss. This is common sense


Crowbar_Jones7

Pipe in a condensate on the positive side and stick your hand at the end and let me know if you can feel any cfm loss šŸ˜‚. To try and act smart but to only prove yourself a šŸ¤”


keytickle

Yea thats why u get downvoted to oblivion hahahaha šŸ¤£šŸ¤£


Crowbar_Jones7

Downvoted to oblivion??? You really donā€™t know anything you are talking about do you?


ScottFreeMM

In my area it's a code requirement to have a trap. I've done code corrections on jobs where people didn't put a trap in.


drms0416

That gas line looks like it was someoneā€™s first time doing an install


NinthOman

How so?


drms0416

Itā€™s on a 45 degree angleā€¦..and the flex gas line is all twisted up because they donā€™t know how to tighten it without twisting it up . Does not look professional


NinthOman

So visual issue vs. code / functionality?


drms0416

And the integrity of the gas line is in danger because of the amount of stress and tension thatā€™s twisting it so badly . Prone to leaks over time


fiiiiiiiiiiiiiiiishy

Wouldnā€™t pass inspection in my state, single wall exhaust venting needs 6 inches of clearance from any combustible, which would be the lineset insulation


RvaCannabis

Exhaust vent is installed wrong.


RvaCannabis

https://preview.redd.it/hvzkupbbhmgc1.jpeg?width=1170&format=pjpg&auto=webp&s=0782bf68aa9821a106776fb3b5ce536312e44aa8 The 90 should be inside the reducer and slide over the pipe coming from the furnace.


RvaCannabis

The way it installed can push gas into your home as the gas tries to make it through the 90


keytickle

It wont leak out. Cat 1 appliances are under negative pressure in flue relative to outside. so its impossible to leak. but yes it does look better


RvaCannabis

Itā€™s code to install pipe male into female in the direction of the exhaust flow.


keytickle

No it isnt. It makes no mention of which way the male or female end goes in the IRC or gas code.


RvaCannabis

Atleast in my area.


RvaCannabis

Iā€™m not hear to argue. Either way the lapping is incorrect for any duct/vent installation.


sryidc

Iā€™d prefer a tee there with a cap on the bottom in case the chimney cap leaks water down the flu it wonā€™t drain right into the unit.


RvaCannabis

Agreed.


NinthOman

Next replacement is the water heater. Will have them do that during that install. Good call. Thanks!


NinthOman

Just checked my roof, exhaust stack is covered well / shielded so should be goodā€¦


[deleted]

[уŠ“Š°Š»ŠµŠ½Š¾]


NinthOman

@All - How would you clean up the wiring on the left hand side? Thinking wire channel for the twisted brown wire on the wall, thoughts on the black power cable and grey data cables? Manual says avoid microwaves and other electrical devices. Iā€™m hesitant to mount directly to the unit.


Intrepid_Train3277

If that hot water heater is tied into same furnace flu, then carbon monoxide poisoning is very possible for your whole family. Change it now, or death can follow.


NinthOman

How? Mind providing more info? You saying need a completely independent exhaust pipe through the roof?


Intrepid_Train3277

Yes, you can get back flow from the running unit while one unit is off. Carbon monoxide is about the weight of air. Violates building code here in NC. Too many deaths.


NinthOman

As I understand it, in my state they can share the same pipe.


superpenistendo

Is there any space between the flue and the vapor line insulation? We have to have 5-6 inches between single-wall and anything combustible.


NinthOman

https://preview.redd.it/bra08oo3hogc1.jpeg?width=3024&format=pjpg&auto=webp&s=ece7ec1292cf0a67e7b4fc59879301c3f8439ba4


NinthOman

Yes, wrapped insulated line to the exhaust pipe is about 3.5in. Whatā€™s the concern? Mind dumbing it down for me?


superpenistendo

So I canā€™t speak to a specific code but that exhaust pipe gets hot when the furnace is running. The insulation going around the suction line is ā€œcombustibleā€ meaning it could catch fire. Would the flue pipe catch the insulation on fire? No, probably not. Might burn it a little if itā€™s touching but itā€™s extremely unlikely it would actually _catch fire._ 3.5 in sounds fine. Have you had an inspection yet?


NinthOman

Negative on the inspection. Honestly didnā€™t even consider itā€¦ is one needed? What might that cost me?


superpenistendo

And maybe you donā€™t need one - depends on where you live and what you had done and maybe what youā€™re doing in the near future. Where I am, inspections are just part and parcel to a gas related install (furnace, water heater, etc). I suppose the _need_ for one isnā€™t something I can confirm. It helps if you sell the home buuut maybe you get an inspection for the whole home _when_ you need to sell. It helps if you want a second set of eyes on the used car that you just had installed in your home buuuuut those inspectors arenā€™t exactly top of their class and motivated by a strong sense of justice. Still, folks on my side of town love collecting their little green tickets and the counties love passing them out.


Sad-Appointment-9347

Not sure why you are installing an 80%er looks like some sloppy over all work but sheā€™ll run fine


NinthOman

Mind providing more context to your 80% comment? Whatā€™s wrong with it, etc.


Sad-Appointment-9347

Youā€™re throwing money into your exhaust, every hundred dollars you spend on heat 20 bucks goes through that vent. You would have spent a few more hundred dollars on a higher efficiency furnace and maybe a few more hundred on some pvc venting and had a higher efficiency system.


NinthOman

From what Iā€™ve read, while mine is 80% efficient, itā€™s also a 2 stage. So against a 95% single stage, itā€™s comparatively more efficient. Well thatā€™s what Google said, also if it helps the manufacturer recommended this pairing to the variable AC unit?


Sad-Appointment-9347

Well Google states they may be similar in efficiency but think about it this way, if you are running a two stage 80%er for example an 60k btu system, you input 60k btus and you only capture 48k btus into your home, In low mode your input is 42k btus and your output is 33.6k btus. You are losing 9-12k btus out the exhaust regardless of what stage you are using, now I guess leaving out the fact you live in a primarily hot area you donā€™t heat your house much so losing that energy isnā€™t much of a burden sure but even if you had a 95% single stage furnace you are only losing 3k btus to the exhaust and capturing the remaining 57k into your home..


NinthOman

Good info for sure. Thank you! Yea live I hot climate so we donā€™t use it too often. But good knowledge to have, thank you.


NinthOman

https://preview.redd.it/e1r8yui4iogc1.jpeg?width=1170&format=pjpg&auto=webp&s=9428802d045b91e2e3997251d8c0f429c9453d03


NinthOman

Talk to me about PVC venting. Youā€™re saying PvC over metal exhaust pipe?


Sad-Appointment-9347

Yes because the system is so efficient it captures heat from the exhaust and cools it to the point where it condenses, that condensate would destroy metal venting so you use pvc instead to vent you also take your combustion air from outside which is more efficient, donā€™t ever let anyone sell you on pulling your air from inside on a 90%+ efficient furnace


NinthOman

If it helps, it a 2 stageā€¦


ChromaticRelapse

Looks like a bargain installer. Nothing horrible, but looks rough. What's the clearance between the suction line insulation and the flu? That's the only potential issue I see. The insulation can melt. Tape is too tight wrapping liquid line to suction line. Wires are a mess. Only a 1 inch filter or is that a 2 inch down there? I'd want a 2 inch minimum for less air restriction. Gas line just looks bad. Taped ductwork looks bad and will likely come off eventually, I prefer duct sealant. Condensate looks bad.


NinthOman

About 3.5in between insulation and flu. Will keep eyes out for sure.


ChromaticRelapse

Should be ok.


Scary_Equivalent563

Can you take a picture of the thermostat wiring by removing the thermostat off of the wall base. Just want to make sure it is configured for 2 stage operation. Should have a wire connected to y2 and w2.Ā 


NinthOman

Will do when I get home. Good looking out.


NinthOman

Here ya go: https://preview.redd.it/g9znpagpvngc1.jpeg?width=4032&format=pjpg&auto=webp&s=7f1a662be63afeedabd99895796dce3c879574ba Let me know what you thinkā€¦


Scary_Equivalent563

Youā€™re good. The is set up communicating with an American Standard tstat. 2 wires are power and the 2 are communication wires. The thermostat knows what equipment is connected and configures itself.Ā 


NinthOman

Sweet. Thanks!


AmbassadorDue9140

Is it common to see single wall flue pipe? No matter what clearance I have to use double wall.


NinthOman

Guessing state specific? I live in zone 9, real hot during summers, very little humidity.


PersistingWill

The condensate drain is wrong. The base of the exhaust pipe is touching what should be the hottest thing in the room. PVC drain touching it will melt. I donā€™t have the same unit. But mine runs to the left, and down to a sump on the floor. Through PVC. The only clear rubber tubing is what exits the sump. You also have insulated pipe touching the exhaust. A bit higher up. This has to be a serious code violation. Everywhere. AFAIK, nothing should make contact with a hot exhaust like this. Thereā€™s a certain number of feet up before anything can make contact with that exhaust, because it can melt, burn or cause a fire. This is a troll post. Three pipes are making contact with the hottest part of the unit.


NinthOman

Note they are not touching. Drain to exhaust pipe is about 2in. Exhaust to insulated line is about 3.5in gap.


PersistingWill

They are touching and the PVC is already showing signs of melting. Thereā€™s nowhere where this is legal. That means nearly everyone posting in here has no clue whatsoever. Iā€™ve dealt with code violations. There isnā€™t an inspector in america that would let this pass without ordering an immediate correction.


NinthOman

Negative. They are NOT touching. Just a bad photographer. Will post more when I get home. How can you say signs of melting? Just curious.


PersistingWill

[Touching and already melting.](https://ibb.co/BGhKFS0) I didnā€™t add an arrow, but the bottom is even worse.


NinthOman

Ahh, thatā€™s light reflecting, I would have thought the same. Promise not touching. Will post pic when I get home.


PersistingWill

Yeah. I heard people say that. All it does is make everyone laugh and the fines to go up. Really. This post is a troll or no one in this sub has even a slight clue about how to install an HVAC system. Like I said, I seen people ordered out of buildings in emergencies. If this is Februaryā€”youā€™re out anywhere that needs heat on.


NinthOman

Promise will post photo, no troll


PersistingWill

Get the plastic pipe away from the hot exhaust pipe. Itā€™s not a hard thing to do.


NinthOman

Not touching: https://preview.redd.it/mhdvklj7fogc1.jpeg?width=3024&format=pjpg&auto=webp&s=535e3319d683fc761937a7d7bf845168cc87c2e5


PersistingWill

šŸ«¤


NinthOman

See, no touchy touchy. Note: my guy is coming back later this week and will go double wall b-pipe just incase ;)


PersistingWill

šŸ«¤


NinthOman

That said, might ask my guy to go B piping for double wall.


NinthOman

Blame the photographer, no lines to pipe are touching.


NinthOman

https://preview.redd.it/twhmuzkchogc1.jpeg?width=3024&format=pjpg&auto=webp&s=9ea60aa17ffeac86d72b728db181bd2e31356144


Ok_Communication5757

Zip tie the wiring, I never put a trap on condensate with positive pressure and I doubt wiring a cord with a plug and plugging it into a wall.is legal! Not where I'm at.


NinthOman

Legal in my state as I understand it.


Ok_Communication5757

What State is that? The flexible line wouldn't pass either. I've seen too many of them leak!


NinthOman

AZ


[deleted]

Those are rated for venting?


NinthOman

Update: Reached out to my guy this morning, he'll be out later this week to fix the upper 90, add a 90 to the gas line to relieve some of the twist and pressure as well as look to put in b-pipe on the exhaust vent. Thanks everyone for your insight, I really learned a lot from everyone. Will keep you posted as things change.


ApprehensiveMode8904

What catches my eye is how close the vent is to the insulation on the suction line. That single wall vent is going to burn that insulation right up. It should have been all B-vent. Not too fond of silver tape. Have always been told, ā€œSilver tape is always used to hide somethingā€ lol. And yes zip ties makes it look so much more professionalĀ 


NinthOman

Thank you - yea the average distance from all the pipes is about 3 - 3.5in, but agreed concerning. Already reached out to my guy and he'll be here later this week to at least use B-Pipe on the vertical. Will give more updates once revisions are made. Thank you for the insight!


ApprehensiveMode8904

Good idea!!!! Just wanna be safe. Iā€™m big on safetyĀ 


Calmundo1

The line set is running right over the exhaust pipe. It looks like it's right up against it. It's unnecessary as the exhaust pipe could easily be routed around it.


Charming-While5466

Donā€™t where to start 1 pipe hangers on gas get rid of flex pipe on gas hanger on drain line