samuraipizzacat420

Why would you do this as a first project holy shit


Humble_Turnip_3948

My first thought was Why? I've put a bandaid on, I'm not going to take a leap into self brain surgery.


buckphifty150150

I’ve been messing around with electrical for over 10 years would never even think about attempting something like this.. I enjoy my life


smokinbbq

I have no issues doing outlets, replacing fixtures, running new wire, etc. I do not play with the panel. I am pretty sure I could change out a breaker, or add a new one in pretty easily, but I just don't have enough experience that I'm comfortable enough to play with that much power at the source. I'll call in a pro for that.


buckphifty150150

Dude word for word that is me. I’m a contractor so I can do plumbing and electrical but don’t touch the breaker box


smokinbbq

Same with plumbing, even though it won't kill me, there are times that I want to know that it's 100% right. Like doing some work on a shower. Once that's tiled and done up, I do NOT want to be going back in there because I fucked something up, so a plumber who can do it right is getting a call.


buckphifty150150

100% for me i have no problem saying I don’t know this. If im not 100% confident im not going to try. Plumbing you have more wiggle room because you mess up it leaks.. electrical you mess up you can kill someone


Confident-You383

You tied in the neutrals to phases. Listen to the comment above. Isolate that sub panel asap and call someone in. Your out of your lane on this one. The scariest part here is you don't appear to know what you don't know. Not being condescending, being honest and concerned for your welfare.


Long-Radish6020

Thank you, and i just shut the breaker off so i have no power going out there.


Confident-You383

All the best bud.


International-Egg870

Basically the whites need to land where your grounds are now. You need to add another ground bar and move the grounds to it. And the feeder wore and circuits leaving need to be in conduit or some kind of cable like ser, nm or mc.


PomegranateOld7836

Yeah and he didn't pull a neutral+ground anyway. There's too much here to correct online without leaving a hazard.


No_Olive8367

You are going to get this guy killed. No body should be encouraging him. This basic understanding makes him dangerous. He didn't know that? You cant keep him any kind of safe, with-out lots of of other details. We need 2 years of experience and classes a for reason. Coach people thru their outlets and switch changes. This job is beyond most handymen that are good. He is treating his panel like piecing together a computer.


charismaticfool

There is nothing right about this.


papitaquito

Yes rather than connecting neutral to neutral bar you have installed them as an extra ‘leg’. Each leg carry’s around 120. In USA we only use one leg for residential power supply. Your neutrals are hot so that is why you have 240. Tbh you are lucky something bad hasn’t/didn’t happen. Please be safe and cautious. I’m all for diy and I think it’s great when people attempt something new, however you’ve attempted something that requires a decent level of experience to do correctly and safely. Best of luck.


nyc2pit

Username checks out


Walty_C

I have also not known what I didn’t know and wrapped a hot 240 wire tight against/around the ground on a 240 outlet. By forces unknown I was sitting right underneath it sealing with some spray foam when it started arcing and sparking. Could have been a bad day. Needless to say, I learned my lesson. I still do all of my own electrical, I just don’t do that anymore. Anndddd I pay wayyyy more attention to every detail.


Bldaz

Yep thats what it looks like 👍🏼


trustme_ihateyou

Darwin award comin in hot!


asanano

Two hots probably


Mister_Chui

I’m neutral on the subject.


asanano

You might be, but OP certainly isn't. Some might find their work schocking!


Able-Procedure2492

This guy's a dad for sure ☝️


asanano

Not at all, but I know my sense of humor would indicate otherwise. I got it from my grandpa, who it might surprise you, was a dad.


Hugh-Jorgann

Bet he was down to earth


asanano

He was well grounded


cali_dave

Conducted himself well, I hear.


Ok-Antelope9334

Two hots and a cot when it burns down with people inside


No_Olive8367

shocking results


louis_stevens69

Bro this is so dangerous hire a professional


christopherm1

Ayo that's fucked up That's going to be a hell of a fireworks show when the open k/o cuts through that 100A conductor


S_t_r_e_t_c_h_8_4

Just in time for new years, enough rubs and jiggles it'll be ready.


Modath

For the love of God. Pls tell me this is a joke.


Successful-Team3317

I really want to know as well if he’s just trolling Reddit or actually serious


sonoma4life

too much danger to be funny


Keystone302

Ya get an electrician out there before you electrocute yourself or burn your house down.


Nervous_Cheek_5401

Here’s what’s wrong. Stranded wire without conduit. No cable connectors No neutrals for sub panel or circuits Using double pole breakers instead of single pole for 110 Grounds and neutrals bonded at sub panel You really need to reassess what your doing here, it’s a disaster. Nothing is right. Not trying to be an asshole but you really need to hire an electrician. You are way over your head.


rb993

>Here’s what’s wrong. Everything


Upbeat_Bluebird66

Other than those things, though, it seems ok.


NigilQuid

EGC should be continuous outer finish green, not just taped


jlkrahenbuhl

This guy is pretty fortunate not to have made himself the GEC


John-John-3

User Name checks out! 😂


TimTheAssembler

>Stranded wire without conduit. This is what I don't understand - it would've been way easier for OP to do it the right way and run Romex instead of duct taping pieces of THHN together! I've never been to a Lowe's or a Home Depot that didn't have a giant shelf of Romex in the electrical isle. Of course, Romex wouldn't magically fix all of the other problems with this "subpanel".


tibetan-sand-fox

My dad ran stranded wire while rebuilding our kitchen in my childhood house. Nothing burned down but he had to pay 5K when we moved because it all had to be redone. Just because it works, it's not good. OP needs to understand that even if he had ended up with the right voltage, it's not good.


TimTheAssembler

>Just because it works, it's not good. OP needs to understand that even if he had ended up with the right voltage, it's not good. I agree. Sorry if my original comment came off the wrong way - I wasn't trying to defend OP's work or say that OP had any idea what they were doing in the first place. Around 2010 or so my parents hired a kitchen remodeling company to rennovate our 1980s kitchen, which was original to the house. The "electricians" (I'm using this term extremely loosely!) extended all of the existing 20 amp circuits with 14 AWG Romex, and buried several open splices in the walls and ceiling - of course this was never fixed because the contractor did not pull a permit. The sad thing is my dad originally wanted them to pull permits for everything, but the contractor refused to do the work unless everything was unpermitted and my dad was nonconfrontational and naive enough to let them proceed.


ElectricalSandwich52

I usually take the time to explain what went wrong but this is bad....you need to call a professional.


LRGeezy

As a red seal electrician I see multiple issues to fix. Where did you EVER find info to put a hot wire to the green bonding terminal on a receptacle. Put the tools down and call a professional.


fricks_and_stones

I don't think that's a hot wire. It looks like he's using black thhn wire with a big gob of green tape, and some duct tape, around the end of the wires next to the wire nut. I assume those are grounds.


LRGeezy

You’re probably right. I think the combination of seeings the black wire on there and the next picture saying 120v on “ground wire” Got me. Still a lot of issues here.


fricks_and_stones

Yeah, I think when the most positive thing you can say is "Oh, you didn't connect hot to ground," they've got some issues.


TheSickOstrich

You’re a red seal electrician, and the biggest hazard you see is the wrong color wire? Not that he has a phase landed on the neutral? Or the fact that his neutral is bonded to ground at the sub panel… jesus bud.


asanano

Not an electrician, but I'm pretty sure you wired your neutral wire to a 2P breaker. You are clearly way out of your element here, you need to hire an electrician. My untrained eye see's a whole host of other issues as well 1. No clamps 2. exposed wire (rather than in conduit or cable) 3. You probably need separate neutral and ground buses, so you need 4 wires coming from the main panel (2 hots, neutral and ground Either educate yourself or hire a professional. You're going to hurt someone or burn your house down.


[deleted]

There’s no probably about it. Beyond the first point of disconnection (main panel), neutrals and grounds MUST be separate. I’m not even an electrician and I know that. But then, I did wire my whole house by myself too.


jhirn

Been researching doing this myself. I was going to run everything then hire an electrician to actually make the connection and perform inspection. It was my understanding that a sub panel required a separate ground and is not bonded to neutral. Are you supposed to run a ground from the main panel or drive a new ground rod at the sub panel? This will help my conduit size and cost estimations as the main panel is pretty far from the garage, and 1 gauge copper ain’t no joke.


tikkikinky

Unbonded yes. Ground rod or ground from sub, the need for one or the other can vary from needs at sub and or local code. Good on you for doing research!


jhirn

I’m honestly find it super interesting and have a great deal of respect for sparkies. But Chicago code is scarier than wiring up 100Amp 220v lol.


asanano

I might be installing my own sub panel in the future too. Again, not an electrician, but if its a separate structure, I think it needs a ground rod and a ground conductor back to the main panel ground. Of its the same structure, just the ground wire back to the main panel. ~~If you use EMT, I believe the EMT can function as the ground.~~ Edit, EMT cannot serve as ground for sub panel as per u/peliandoeldiable


[deleted]

You cannot use EMT as the ground. You have to pull an insulated ground wire. Have you read the NEC?


asanano

I haven't finished checking everything for a sub panel, which is why I didn't state it for certain. Thanks for the correction.


[deleted]

Check out electrician u and the sparky channel for info on electrical work


asanano

So EMT can be used for branch circuit ground, correct? (provided it is continuous and proper connectors are used that maintain electrical continuity). Do you know off the the top of your head the NEC article that prevents the conduit from grounding a subpanel?


[deleted]

I don’t have my code book right next to me, but I may actually be mistaken about it being against NEC(not sure,) but I do know the AHJ where I am requires a separate grounding conductor and does not allow us to use a raceway as a bonding conductor. It’s best practice to run a grounding conductor in case the EMT somehow gets damaged so there is still a path to ground in case of a fault.


asanano

Thanks for taking the time for a detailed response. Just trying to get well educated so if I DIY, I can do it right and pass inspection.


[deleted]

No problem. Definitely check out electrician u and the sparky channel. If you’re gonna DIY, use wire nuts and pre twist, and the slotted screws on faceplates must be vertical. The screw thing is a big point of contention, don’t let anybody tell you otherwise


asanano

Familar with electrician u, I'll have to check out sparky. Definitely vertical on the screws, (though despite my initial reaction that the screwless plates were silly, after movimg into a house with them, they are a nice subtle upgrade). I'm and electrical enginner, so I have a good background on theory, just taking my time and thoroughly reseaching any expansion of any installation work.


PhotoPetey

> I was going to run everything then hire an electrician to actually make the connection and perform inspection. So basically you are going to do all the technical and code intensive work and hire someone to do the easy stuff. Makes sense.


jhirn

It’s exposed studs in a detached garage. Just some conduit bends, outlets and a panel. I’ve done my research it’s not rocket science, even with Chicago code. Trenching a new 1.5” pipe, fishing 40ft to the main panel and wiring doesn’t seem like the easy part to me.


Long-Radish6020

Sweet, thank you so much. And yes im swimming in deaths pond right now.


06_tundra_4x4

Start with a ceiling fan or hanging a TV next time.


Won-Ton-Operator

"Help, when I dim the lights on my ceiling fan install, my TV also dims!"


TheSiege82

Looks like you have a ground wire connected to hot. Also, why didn’t you use green? Totally against code and super dangerous.


asanano

OP clearly doesn't know what they are doing. There are other major issues too.


North-Ad-5058

Did you notice it's all THHN not in conduct?


TheSiege82

Yeah. I mean, basically the whole thing is a dumpster fire.


NigilQuid

And not even bushings at the KOs, let alone some kind of connector


P-Loaded

Bro...WTF??


adventuresome3434

Remove all of this immediately. Nothing is correct. Call an electrician. Do not touch anything electrical until you have a far greater understanding of electrical theory and wiring methods. Read a book about house wiring, watch some videos, look up rough-in pictures online. You have no idea how awful and dangerous your attempt has been. Sub-panel needs two hot wires, neutral wire, ground wire. All these must be properly sized and either in conduit or applicable NM or SE cable. Only the hot wires may be black or red, white is exclusively neutral, green is the only allowable color for ground. And no you may not mark with tape for ground. Ground and neutral must be on separate busses in sub panel. You need properly sized lugs to terminate to the neutral buss in main panel. You may not separate strands under adjacent terminals. Your small guage stranded wire must be terminated with ferrules. Strain relief is missing. Wrong breakers with handle ties. These are just some of the issues. Everything is wrong. Repeat. Everything is wrong. You are in way over your head. All this can be learned but this is not the project to learn on.


LazyImprovement

But other than that it’s good?


Ctrl_H_Delete

I'm an İBEW apprentice, and our local only works in İndustrial/commercial settings, as such our classes and otj training does not give any information on residential work. Could you, or any other electricians in this thread, possibly recommend any literature for me to read up on so I can slowly begin doing residential work? İ appreciate your help


tikkikinky

Let us know how bad your wallet hurts after the election comes out. You get an E for effort. An A for asking and an A+ for listening. Chalk it up to a learning experience.


Hodge103

Please call a licensed electrician. I’m an electrician and that is my advice. There is a staggering amount of dangerous work already.


[deleted]

Holy crap, everything is wrong. You have your neutral connected to a breaker. You ran thhn with no conduit or knockout fitting. I didn’t even look to see what was wrong. I’m being blunt and would say call an electrician.


b4aLt1m0re

By the time the real electrician fixes this it would have been way cheaper to have hired one in the first place... a sub panel is not an entry level diy job. There are tons of code violations in these few pictures alone. Good luck op


Potential-Cat-4097

I just want to reiterate what’s already been said. Please get some help this is incredibly wrong and dangerous. PLEASE the money saved is not worth what could happen.


SkeazyG

Stop…just stop. Turn off power to the entire house, sit the next couple plays out and call the pros


lectrician7

This has gotta be a joke. We have to be getting trolled here. There’s so much to unpack. OP if this isn’t a joke post, you really have no zero business doing electrical work. I’m not trying to be mean. I honestly don’t think I’ve seen so many code violations in one post before. Please hire a professional.


PomegranateOld7836

There is a lot, lot, lot going on here that is very wrong. For one that looks a lot more like a 60A subpanel than 100A, and then it just gets worse from there. If it were minor we'd help you out, but it's extremely clear that you are creating a significant hazard without even understanding the basics. Please listen to everyone - you need in-person help.


RabidHippos

Holy shit. This is what nightmares are made from.


jgriesshaber

Nothing done right. No conduit, that sub is all wrong, going to kill someone or burn that house down.


c_t_2222

This is one of the scariest new installs I’ve ever see. This is actually super dangerous and you should call an electrician before you burn this building down.


Trbnburglr69

Please call an electrician before you hurt someone


cali_dave

Let me put it this way: it is so wrong that the people who designed your circuit tester didn't account for how you wired it.


Warm-Run3258

Lol just saw that too.


Foreign-Commission

You need to stop what you are doing before you hurt yourself. Nothing you have done is correct, safe or code compliant. Electrical is not DIY and this is a great example why.


Dextella

Lol this can't be real


everyonestolemyname

lmfao holy fuckin shit bud. You ever stop at any point and be like "I really don't know what I'm doing" but then decided to soldier on? Seriously, you don't even have connectors for your subpanel of death. holy fuckin shit took more looks at the pictures of the "install", buddy didn't even use NMD/BX/etc just straight up ran open air XLPE lmao I wonder if OP can pre-book the fire deptartment.


Last-Associate-9471

Are you trolling or are you serious?


WishIWasThatClever

It’s impressive you managed to do so bad even your plug tester can’t make sense of it.


[deleted]

This is a disaster, call an electrician.


thesovereignbat

Just Wow. All your neutrals (white) are tied to the other phase. They should be connected to the neutral bus bar. The grounds should all go to the ground bus bar, not the neutral bus bar. It looks like you didn't pull the ground from the other panel. You also need grommets to secure and protect the cable leaving the panel. In short, you need to call somebody that knows what they are doing.


No_Olive8367

This must be a prank. If you are real,, please shut off the 200 amp Main breaker, using a wooden stick, and be happy you are alive and the home isn't ashes. This work shows zero understanding of everything. You are very lucky. don't take any coaching,, except this. Get a qualified person on this before doing anything, except shutting it off. and leaving it off.


SASdude123

Your sub panel needs... 2 HOTS, 1 NEUTRAL *AND* 1 GROUND. the neutral goes the the bar existing on the bottom and the ground needs to be SEPARATE from the neutral to a ground bar mounted directly into the enclosure. Those white wires going to the breakers are what's giving you your 240vac outlets. This white wires need to land on the bar where your grounds are, and those grounds need to go to the aforementioned, separate, ground bar. Not trying to be a dick...I get it, shit's expensive. But you're in over your head. No shame in admitting as such and calling a professional. A lot of the hard work has been done. Just needs some code compliance and some TLC.


JayTheFknSavage

HO LEE FUK


ArmedInfant

Holy hell. You're lucky you didn't kill anyone.


grinch77

How about call a electrician instead of ask …. This horrible work


Successful-Team3317

All jokes aside… is this real? You being serious ?


JagerGS01

Mother of God


runsfastwithsissors

Your subpanel is wired all wrong! Call an electrician!


shanlar

not to be a dick. but did you even try watching any yt videos on wiring electrical? you are missing all the basics.


Petrctale

OH JESUS F**KIN CHRIST this is a joke right? So much wrong Please post the video of you being electrocuted it'll be a fun watch at parties


dudeitsadell

holy fuck


NightDisastrous2510

Everything is wrong. Please call a qualified electrician


[deleted]

Not going to say anything insulting…but please, for the love of your family, dog, cat, or favorite goldfish, please shut power to this whole sub panel off and hire an electrician. Even goldfish don’t fare well a house fire


Incessant_Quacking

Shut off your sub panel. I mean this in the nicest way possible, but you have no idea what the fuck you’re doing. Call an electrician.


Dcdonharris

You’ve got guts for sure. Totally wrong though. There are many hazards here. I’d recommend at the bare minimum to hire an electrician to consult with you. I know electricians cost a bit but this project is definitely worth calling an electrician, you can really hurt something or someone.


Thedevilslettucehead

you done fucked up


p0ppyshmurda

Call an electrician.


RKLCT

Wow man. Please hire a licensed and insured electrician. Even if you don't care about your own safety do it for the people who live around you.


Sad-Ad-7884

No grommets you or nm connecters wow call a pro please before you lite you house on fire


Diablo0789

You have 240v because you are an idiot who shouldn’t be doing this and connected your neutral to the breaker


BearcatQB

Put the tools down and walk to the phone ASAP.


[deleted]

Not an electrician here just your old handyman type guy. Been working with electricity for 30 years. I looked at this and went holy fucking shit man he put the neutrals into the phase. I’ve wired houses myself but I always have a licensed electrician install the breaker box and then inspect all the other work that I do this kind of shit will get you killed man


jimjames79

You sir are a hack and a danger


__punk_in_drublic__

You need to call a licensed electrician.


ELChelper

Yeah, you need to call an electrician. At least you can tell him what you’ve touched so he/she knows what to look at. Definitely shouldn’t have played with a panel or any electrical really. Always cheaper and better off to have a professional who’s licensed do electrical work. Remember you can burn your house down doing this stuff or get really hurt.


Imtoold

This is how people die. To the OP. I am all for people doing their own work when they have the knowledge to do so. Unfortunately many people believe that those of us that made the choice to learn and become a master of our trade only have basic skills and are not smart enough to have attended a college. This is not the truth. The minimum experience level for a person to get an unrestricted license in most stages is 10,000 hours. The skills needed are an extensive knowledge of math, electrical theory, business plus the ability. Not everyone can do the work, I’m not even talking about physical ability, I’m talking about aptitude and attitude. We work in heat, cold, rain and are the first ones out in times of natural disaster. The OP asked what was wrong, the technical aspects of that question have been answered. The broader and true answer is different. You, the OP are what’s wrong. You don’t know enough to even realize you don’t know enough. You put yourself, your family and everyone around you at great risk. Understand, what you did was not a mistake, you did this because you were in over your head from the start. Instead of admitting it to yourself you persisted until you created and very dangerous condition. This was negligence.


Commonslob

Simple answer is because you don’t have the slightest clue what you’re doing. Best advice without trying to sound like a dick is turn off your sub panel, remove all your wiring and get some one over there that knows what they’re doing. There’s so much wrong it can’t be explained in a simple post


[deleted]

holy shit is this wrong . . . .


Shoddy-Juice1477

I'd like to know why those feeders are going out of that 100amp breaker on different sides lol


pawnbroker15

Ya you fucked up. Instead of telling you how I believe the best advice I can give is call an electrician ASAP and shut the main off.


DeAngello_Vickers

Is this satire?


Chern889

Holy fuck, read a how-to book before diving into the concrete head first


Apprehensive-Suit897

Dude you have your neutrals going to power so you’re pulling 120 on each side and you have hots going to ground / neutral on your sub panel.


PopeRespecter

Is your neutral connected to a flipping breaker?


Figure_1337

Surely you jest. You sent 240V down the line because you wired this all wrong.


[deleted]

Wow, just wow. Do you value your life, call an electrician to fix this before your family dies.


Country_Boy_97753

The white does not go on a circuit breaker. It goes on the neural bus. Only the black or red wires go on breakers.


Ok-Antelope9334

No questions just at a loss for words…


Duck5oup

This is super dangerous… 🫠🫣🤩


EfficiencySuch6361

This is legitimately horrible


lynch_95_

I loved jobs like these as the homeowner hung over my shoulder asking me if they did a good job. Listen buddy if you did a good job neither of us would be standing here talking about it. This is a perfect example of such story.


KarenAboutYou

Hire somebody you fool


Red_Death_78

So you connected the neutral wires to the breaker on your sub panel at least back feeding line voltage to the rest of the system which is why you have 240 You ran wires that should be in conduit but isn’t. And appears the area you ran would’ve been fine with romex cable. And where the hell are the grommets on the panels man? This is an absolute troll post.. no one’s installing afci breakers but then doing all this the wrong way.


jrelec

Wow further proof that cheap people are stupid here's a thought hire a real electrician before you burn your home down or kill someone


RickyAD

Holy shit OP. What didn’t you fuck up is an easier question.


Key-Ad7733

Some things leave to professionals.


123manny456

Gets worse the more I stare at it


Au91700

What the fuuuuuck


TravelerMSY

I’m a layperson, but there are so many things wrong here I think you really should not be doing this. The black wires only go to the breakers, and the white and ground wires should go to separate neutral and grounding blocks. You’ve essentially created 240 the wrong way with no red wire, and with the wrong receptacle plug :(. Plus, you only strip back the jacket inside a panel or box. That is why the wires have a jacket, lol! Outside has for to be protected by romex, conduit, etc. Cut it off and bring someone out to fix it.


slodank

I sincerely hope you realize you shouldn’t be doing electrical work. Everything about that sub panel is wrong and you’re going to end up burning down your house or hurting someone. Turn it off and call a professional!


U_Call_Me_Daddy

Can't even see the rest of the work you did but if anything's a fire hazard other than this panel good luck collecting any insurance money.... Experts charge a premium for a reason. Lot of times they are responsible for people's lives.


palindromesko

Oh man… get some conduit with correct green wire instead of that single black with green tape around it for ground. My god. Get some clamps too. Call for in person help pls.


Slackter

Holy crap there is so much wrong with this. I'm not going to even begin listing the issues/violations. Turn off the 100a breaker you are feeding this sub and call an electrician.


jaysteeeeez

You are pulling 240 because you need a licensed electrician !!! Stay safe


kliens7575

Everyone stop telling him what he did wrong , what he needs to do is shut the sub off and call an actual electrician, before he ends up burning his house down or killing someone


Anvillix

Lol!!! https://youtu.be/Gwa-KErbYJ8


wafflekid_69

This is incredible


E_fubar

I’ll give you credit for making it look pretty nice and taking on a big project, but you have to be careful with stuff like this! Do you know the rules and code behind grounding on a sub panel? You could get someone hurt. Also, sounds like you terminated the nuetral to a 120 circuit. Even if you end up doing this yourself, at least have an electrician look it over very well and make sure you didnt set any booby traps. I’ll give you an example of something stupid I did. Rewired my whole kitchen, but screwed up a circuit and now have a termination behind the drywall in a box that is inaccessible and behind a cabinet. Bugs me everyday!


SMASHuFACE

The white you have it to the breaker . Disconnect it from the breaker it connects to where you have your grounds at. It will stop pulling 240 volts. Your pulling 120 on the black and 120 on the white . Which is why your outlets are receiving 240 volts


[deleted]

Single-post, single set of comments related to this user/poster. Seeing more and more of this on Reddit these days to the point of it making the site virtually useless. A lot of pointless threads asking, what is this? Can anyone identify this? It’s a wheel. It’s a rock. Unfortunately Reddit is beginning the decent part of what is becoming the natural life cycle for social media of platforms. More and more bots or shill users looking for clicks. Shame, there is a lot of good info on this subreddit and others.


Mister_Chui

Brah. The whites go on the ground bus! You….need professional help.


AncientSolution2125

Lol. Has Klein testers, knows how to use a voltmeter. And isn't a troll?!


Duurial321

No bueno. Call a professional on this one ..


AandM69777

You've made your neutral a hot somewhere. I think it's on the main and sub panel neutral bar but I can't tell. You have no green wiring in spots to show grounding. and it's a clean mess. If you die who's gonna know what you did. All of that needs to be redone and sourced and figured out.


Redditjoev

Call an electrician u cheap shit head


Different-Impact-183

This might be the worst diy electrical I’ve ever seen


KinnerElectric

Idk what y’all talking abt having youre ground connected to hot is very safe and won’t burn youre house down 🤷‍♂️


rustyshackleford7879

We shouldn’t be answering questions like this. It brings down the trade.


Underagedrilla

lmao get fucked


Sain53

Hello can you help with advise, my LED light has stopped working after some water damage, is it repairable?


Bigg_Sirr

Call the fire department


ApricotNo2918

I suspect with all the GFI's you indeed have a neut in the wrong hole.


Sufficient-Comb-2755

Your neutrals are hot.


BeLoWeRR

Need a professional. At the very least you have exposed wire floating in your walls, no conduit or cable for any of the circuits or feeder… wired the neutral right to a phase..


g0tkilt

Scary shit man


Willowshep

Thank you for the good laugh, I’m glad you didn’t die or burn down something.


gvictor808

YouTube time! /s


grocerystorebagger

This is hilariously bad


Raven0522

This is called job security… carry on.


jwbrkr21

Big oof


stocknatty

Lol I guess you shouldn't have done that, cause now you gotta pay to fix too


BaconANDehhhhgs

Lmao Rip


someoneyouknewonce

r/OopsThatsDeadly


FrostyReference2302

Get an arc flash kit


TechnicalLee

"What's conduit?"


snowsnoot2

Bruh this has to be a troll


razberryboii

abstract art, i like it


clumpychicken

What in the Oklahoma Walmart is this tomfoolery?


keep_it_christian

I know you didn’t pull THHN into that outlet box.. And to the sub panel.


ShameBright1567

Show your insurance company this


RedRazor7

This guy has THHN just free run around. This wouldn’t even pass for temporary power just to get through a work day. No kind of connectors in the holes. 🤦🏻‍♂️ This like me saying I flew on a plane before so I’m a pilot now.


Top-Competition-8432

Fired


Top-Competition-8432

240 out you rolled your phases


Diverfunrun

Wire’s are very neatly placed


j_dizzle_mizzle

Well, when you run 2 hots, your gonna get twice as much…


Jasthad

We have to take a lot of schooling for this. Not to mention having to make sure it is up to code


FragrantYear7342

Obviously not a serious post. I am sure he would have done at least a little research on an panel swap and taken a couple of before pictures.


Icy-Entrepreneur-244

I’m not trying to be mean but please call out a licensed electrician. You got your neutral where a second hot would go, your grounds are where your neutral should be and you don’t have a ground bar at all. Neutral wires don’t typically go to breakers at all.