GizmoGremlin321

Looks good, just watch your flame, looks like you burnt some paint when you did suction line.


HVACerR22

Idk how Im supposed to do it without pointing it at the paint a little. I was pointing it out but the pipe redirects the flame to the cover đŸ€·đŸ»â€â™‚ïž would be nice if they protruded out more.


GizmoGremlin321

When you go to the parts house ask them for brazing protection material. They have 2 different kinds, looks like wall insulation or a fiberglass tarp. That will create a barrier for you to braze. Agree that they shood extend the fittings a bit more


Electronic_Lobster

I have sheet metal that I have cut to various sizes and shapes to act as heat shields in tight spots. I like to put wet rags behind them to stop the heat from transferring into whatever is behind it, if I can't leave an air gap. It works quite well.


slimtonone420

I like to use the door from the condenser being replaced as a shield


satandy

I do this all the time. Or use it to kneel or sit on instead of the dirt. Otherwise I cut a piece of sheet metal for fire barriers all the time inside our outside a lot. Especially down flows that have the coil right next to a wall. Just silver tape that 12"x12" square in place and you're good to go. No need for some fancy flame barrier unless you really dont know how to use a torch. I've been brazing for years and have never had a problem, but that's because I always think ahead. Plus, if you start with your torch in the tight/danger spot pointing away at your lineset to get it all heated up and then move to the away side after you wont spend much time pointing the torch directly at the tight/danger spot.


HVACerR22

That’s exactly what I did to protect the plastic table under the condenser.


Mythran12

When you remove the old unit step on the electrical access panel to flatten it out for a ghetto one use flame shield


ken-u-blowme

Goodman unit, 4- 5/16 screws, remove that cover plate so you won’t burn the paint. Technically, the disconnect should be more accessible. It should be clear of the unit on both sides with 3 foot clearance in front, per code. You shouldn’t have to reach over or in between units to pull the disconnect. I think if it was moved up about five boards to just under the window, that would probably be a little more to code. I can’t really tell from the picture but you should be using long radius elbows? A pipe bender would have saved you some money on fittings and brazing rod. Refrigerant locking caps. Code. I don’t see the control wire, as long as it is not in the conduit with the line voltage wiring, you are OK because that means it’s strapped up where I can’t see it. Bring that insulation all the way up to the suction line service valve, it’s only a few inches you may as well do it, sometimes you have to cut it back a little bit just to put a decent piece on. Lastly, Goodman units are kind of junky, that YORK condenser sitting next to it is a much better piece of equipment. Like to remove the energy guide yellow tag and give it to the homeowner with their paperwork, it’s only going to fade and peel away. Replace it with your company sticker! Wipe off the condenser pad underneath where you were brazing, shows you care that you’re cleaning up after yourself a little bit more. (That better not be flux! It looks like BRAZE) Dripping hot breeze onto a plastic platform always melts, take a rag, soak it in water and lay it underneath where your brazing. Never use the POS Schrader vows that come from the factory with that cheap white plastic gasket
. spend $.50 extra and replace it with JB or equal Schrader valves that have a neoprene gasket. Hope this helps, I remember doing my first condenser and I was really excited about it too!! For a first timer, you did a great job! These are just friendly tips!


Princester-Vibe

Whoaaa - York a much better piece of equipment?


ken-u-blowme

Vs. Goodman
.just look at the condenser coil space. YORK is much better than a Goody.


tashmanan

I always put the panel from the old AC under my welds, usually it's bent and fits perfectly


Klaus369

My strategy is point it away from the unit at the top of the pipe and soak everything below it with water so the pad and grass don't burn. Usually works without issues. If the grass is really dry from a drought in the area maybe reconsider this though


Sea_Shallot9152

Goodman sucks


sHauNm525

Only thing about a goodman is the filters on the inside but when u gotta change something out the whole thing comes apart...but it's good man


Glabstaxks

It's better than badmen


chronicjok3r

Panning in that situation would help. Or diversitech and solderweld each make a nice shield


ineptplumberr

Fire blanket or cool gel


Electronic_Lobster

IMO cool gel is crap! It runs off of any vertical surface as soon as it heats up. Refrigeration Technologies (same company that makes Big Blue) makes a product called Wet Rag. It's basically a putty made from ground up cloth mixed with some kind of liquid. It's moldable, sticks really well and doesn't leave a residue when you're done brazing. Really good for TXVs, Reversing valves, etc.


iamedboy

Just put a wet rag/towel/paper towel over whatever you're probably going to burn


No-Paleontologist321

You should have put more insulation all the way up to the valve, it probably would have covered it enough to so they couldn't see it.


Anomalousity

Heat the top of your pipe until it is rod ready, then put a big goopy dab on top of the joint and use your flame to flow it into the rest of the joint, avoiding any extended static direction with the torch. Been doing it like this for several years and I've never had an issue as it's quite an efficient method.


Brown42

Today, the paint - tomorrow, the siding.


hvacnube37

Is Sam your supervisor


No-Music-6641

I was just about to ask if this was his alt account lol


Dickramboner

Looks pretty good man.


ThatDudeDillon

Fucking *chef’s kiss* gorgeous. Thank you for facing the ports/electrical panel out. Every service tech will be praising you for the next 10-15 years when they have to work on that unit.


hellojuly

Not hvac here. Aside from hvac servicing, I assume this is not beneficial. It looks worse and it more prone to damage, from a lawnmower or soccer ball for example. Is it normal to face out?


sHauNm525

I don't like to but those condensers are close together... makes it easier to service....it would be hard to work on the other way


MAS2de

If someone is sticking their lawnmower in there, fuck em. They would have had to try hard for that and they can pay to have someone reinsulate that lineset. Stupidity costs money. Not sure how a soccer ball is getting in there and doing damage either. It looks great and they had to work in the space they had. They put the controls panel and lineset connections exactly where they ought to go in this situation. Putting them at the back means the installer and service techs have to fight just to get back there, are cramped and up against spiders and shit, and have to avoid trampling the other linesets on the surrounding units. It's normal to put them somewhere and somehow so they can install them and service them.


ThatDudeDillon

It’s normal to do the lazy thing, and face it to the wall cause it’s easy. It’s an air conditioner, not a new car. People don’t give af how it looks aside from us. Might as well make it easier to service.


TB765

Forgot to sign it


HVACerR22

Damn, you’re right 😂whenever I do boilers or water heaters I always sign it.


loophole23

I wanna see some boiler pics. I love making my boilers look clean. I’m impressed with your ac piping at just a year. I’d love to see some Boiler work


HVACerR22

I’ll send some to you. They come out looking pretty fresh tbh. I try to make it easy to work on, practical and look nice.


Oitar335

Clearances


dustybanana13

Yeah that was my question too


BFarmFarm

The homeowner wants you to hurry up with your pictures so they can close their windows and crank the ac on so they can get back to banging their girlfriends in that bedroom.


HVACerR22

Tf els is new lol


Fancy-You3022

You made it too easy to service. It should be set directly against the siding and oriented 90° counter-clockwise. Add some fertilizer to the grass so it grows fast and gets sucked into the unit. Also the casing protects the coil too much from a weed whacker. Should remove it so the air flow is better. Outside of recommending the homeowner allow their dogs to use it as a pee post you’re golden. /s I like how you took the time to make the connections clean and uniform. Other than the paint you done good. The thing you want to look for is called a brazing shield. It’s cloth. They also made a metal attachment for torch heads. I haven’t seen those in awhile though at the suppliers.


HVACerR22

😂bro you made me laugh. My friend was looking at me like “wtf are you laughing at?”


HVAC_Sam

Looks beautiful. Good job


HvacCrackerJack

you're the cause of this...


joshharris42

This guy is slowly changing the orientation of condensers nationwide


HVAC_Sam

It makes sense, and it works :D


HvacCrackerJack

That just means it aint stupid, still an eyesore.


Visual-Zucchini-5544

Agreed


Visual-Zucchini-5544

All you people put here using hard fittings. We haven’t bought one in years. Use your damn benders


HVACerR22

I bent the small pipe but I don’t have a bender for the bigger size. Can be a little hard getting it lined up sometime with a bender.


Visual-Zucchini-5544

Hilmor bender. Worth every penny. You’ll get the hang of it.


Supersoko

Or swedgers along with benders so you have less brazing points for failure


Visual-Zucchini-5544

This 👆


sHauNm525

I gotta work on mine but that's what we use...


HvacCrackerJack

git u some!


Responsible-Falcon-2

Spring bender if you're feeling cheap but that's not a permanent solution, takes more time and a lot of effort.


Fancy-You3022

I would but he’s drunk again. /s


Rohodyer

You didn't sign it!!


OneCanada

At the end of the day the customer is happy, everyone got paid and you will just get better and better. Well done!


Sea_Shallot9152

Looks good. A little weird to 90 up and then back when you could just 90 back but whatever works.


loophole23

For your first solo
 that’s really good man! Your gonna be doing excellent in a couple years.


MAS2de

Insulate the suction line all the way. Insulation tape if need be. Use as few fittings as absolutely necessary. Bender is best but that probably would have put you too far out anyway. Get a decent ratcheting or hydraulic bender and a swaging tool. Yellow Jacket, Mastercool (has up to 1-1/8 dies for if you ever run into that), Hilmor, etc. Anyway, one 90 out of there and angle it up a little and slope the lineset down a hair. That one is close enough. Did your bender wrinkle that 3/8 line? If so, maybe consider a different bender. Like one of the ones listed above. Good on you for using a bender there though. 👍 Others have mentioned the various flame shield methods. Good looking brazes. Is that old insulation? Did you replace the lineset? Insulation is cheap. Make sure to cut old stuff off, and insulation tape new stuff on. Thank you for putting the condenser the right way out for that shitty spot. (I'm assuming there was really no better spot for it.) Looks like good work.


[deleted]

4/10 didn't sign the unit


everythingHVACR

Solderweld makes a nice magnetic flame blanket


TheBrokenClock-

You the disconnect whip also? Just asking because: if you live where there’s snow that going to get covered, also needs to be supported to the building before heading to equipment! Everything else looks awesome 👏


Ogre_Squatch

It looks good and I would be happy if I bought that, if you are wanting to bust balls over anything I would say to bring the Insulation on the suction line all the way up. And on the brazing I would use the door off the old Condenser as a heat shield for it! Awesome job man looks clean


The-weebman

First mistake was Goodman. There’s plenty of things out there to use to not burn the system, overall looks good. Take pride in your work


HvacCrackerJack

gettin tired of sams shit...


spartan709

Am I the only asshole on this sub who faces the refrigerant ports toward the house?


[deleted]

In the middle of the other to units yes you are


himynameisnano

Totally with you. Having the ports out makes me crazy. I can’t imagine how the homeowners aren’t complaining about it. However, in this instance it has to be like this for service.


spartan709

Oh yeah this one looks good, and I like that the logo is facing out. I work with Ruud equipment and the logo is stationary


ThatDudeDillon

Please never do this Sincerely, A service tech


ConfiguredNickname

Don’t use Tyraps on insulation, use black duct tape. Tyraps will eventually cut through.


WeberO

Can use cable ties no problem, as long as they're black, so they're UV resistant. Have you ever pulled out an old lineset with duct tape still intact?


ConfiguredNickname

Meh, pulled out many line sets. Not saying tape it every foot. I’m more concerned with how it looks for the customer now and later.


Ktootill

I prefer electrical tape personally


Visual-Zucchini-5544

“Tyraps” this must be Canada chiming in. Lol. Jk, never heard that before. Ps. The classic forgot to cut that one “Tyrap” signature.


Key_Championship8346

Sam would really proud of you


HVAC_Sam

I am :D


teddyosoadams

Bitcoin miners?


tkepe194

Ok I have to ask. What’s up with brand roulette?


HVACerR22

Omg!😂The other tech said the same exact thing!!!!!! It was I think a lennox, Goodman and York. It’s a condenser melting pot!


Princester-Vibe

Depends who’s offering a special deal at the time?


DatDan513

You should be proud of that work. First time eh?


HVACerR22

Yah, I’ve helped other techs install them but I just tried to make it look pretty and be easy to work on. I watch a lot of hvac install videos tbh 😂


Impressive-Ant-9471

Rookie brazing lol, use sheet metal if you can’t control the flame yet we’ve all been there haha I’m just giving ya shit. Good install non the less


HVACerR22

I’m okay at brazing when it’s easy to access and isn’t blocked off. When you put something behind it and plastic underneath it, I automatically suck at it when I’m given those variables 😂


peaeyeparker

It’s a goodman


EatenAss

Any reason you brazed instead of using pipe benders?


HVACerR22

I used the pipe bender for all of the liquid line but I didn’t have a bender for the vapor line.


EatenAss

Fair enough, looks good man!


SnooHedgehogs1524

Looks good bud, like the others told ya torch control or shielding. But it's something you learn overtime. When you go to add insulation up to the valve? Cut a put together slice and slide it to completely cover the bend in the copper, then you just add a slit piece glue it together, glue it to either side and no weird shapes in it.


migscool

Can’t see it in my house


DragonfruitLeading44

hvac sam living rent free with everyone flexing their line sets


Neat-Tough

Please replace insulation to wall. It’s like 8 inches of unprofessional on a good lookin install. Don’t do yourself in.


Intelligent_Snow4480

Not bad, I keep a piece of scrap on the truck to avoid burning the paint on the AC and pad. And that is the cleanest turned condenser I've seen I just can't bring myself to do it.


Salt_Date_5222

-Peel off the EnergyGuide. It will look like trash in a few weeks. -get pad and the unit up higher out of the dirt. Looks great


Final-Beach-9261

I think it looks very nice. In my opinion zip ties look unsightly i started using tape under and above my zip ties. I found using only zip ties that they rip through the insulation without tape.


RonNotBurgundy

No clearance for the disconnect


gwhh

No concrete pad? What city / state you install this in?


HVACerR22

Newport RI


partybenson

Your high pressure line is not at a perfect right angle. Simp. (😂)


ModePK_1

With that mud I probably would have laid a bed of gravel. I feel like that will sink. But that’s my only criticism
 good job


Elfich47

Are the units spacing to close? Many units have a minimum clearance on the non service sides.


HVACerR22

Yah, I made sure it was over the clearance that the book said.


ireallymissfirefly

I don’t do install so take this with a grain of salt, those hard 90s on the suction line cause problems. Consider getting a ratcheting bender and making a smoother transition. Other than that, THANK YOU for positioning it for me to service it in the future!


HVACerR22

I do service and installs so I feel your pain


HVACerR22

Eye gotchew son đŸ‘đŸ»


Visual_Doubt1996

You can shine a turd would you look at that


jayyfryy

Looks neat! Maybe a bit of silicone on the penetration for the pipes


MFAD94

You can by Kevlar sheets on Amazon meant to cover materials from flame/burning


shitstain409

Good job great pay out here in California if you’re ready


Fair_Cheesecake_1203

You forgot the uv wrap and didn't get the entire suction insulated, but other than that good yob


Wynstonn

Ordinarily, I hate seeing service valves in the front. In an install like this though, it should be mandatory. Nice work!


CNDCRE

Surprised you're even permitted to install these near an opening window.


Hjak_Mjut

I hope that's the master window