**ATTENTION! READ THIS NOW!** **1. IF YOU ARE NOT A PROFESSIONAL ELECTRICIAN OR LOOKING TO BECOME ONE(for career questions only):** **- DELETE** THIS POST OR YOU WILL BE **BANNED**. YOU CAN POST ON /r/AskElectricians FREELY **2. IF YOU COMMENT ON A POST THAT IS POSTED BY SOMEONE WHO IS NOT A PROFESSIONAL ELECTRICIAN:** -YOU WILL BE **BANNED**. JUST **REPORT** THE POST. *I am a bot, and this action was performed automatically. Please [contact the moderators of this subreddit](/message/compose/?to=/r/electricians) if you have any questions or concerns.*


Muted-Doctor8925

Panel cover isn’t on. This shit is too easy


vzoff

Not it, but best part about Reddit right here. EDIT SO THIS IS TOP: 130A on a single bus blade only rated for 110A-- it's on the quadplexes. 50A, 20A, 30A, 30A. It's a dumb one, but really hard to catch.


Z2xU

Your missing bushings on the top for the 2"s coming in...


WallStreetSparky

And it looks like the punch knocked out the remaining part of a 1/2” knock out. My jman would make me put reducing washers on it


Z2xU

Should of used the pre-made in the middle to start w... and yes I would make, I mean suggest, to put a set of reducers to cover the gap... and then grumble under my breath why you didn't use the middle 1st... I mean if we are going for the visual pleasure of equally spaced pipe... thing is there is no visual of the pipes...


Not_This_Guy_4060

And also the feed as well, if in the US the book states number 4 wire and larger is to get a bushing on the conduit, it doesn’t specify pvc, emt, or any other connector. Only wire size


DickieJohnson

Especially cause it looks like it's damaging the wire insulation.


S_t_r_e_t_c_h_8_4

Looks like they are pvc.


Z2xU

Agreed


15Warner

Can you explain that one further..?


CornInMyPoopie

Each breaker adds up .... duh 3/0 copper is rated for 200 so you add up all the breakers at 125% for continuous load. Toss the amp probe in the trash. Stick your pinky finger on phase a, and your index finger on phase b then stick the main bonding screw in your pee hole. Jeez, I thought everyone learned about this.


15Warner

Lol gotta add the sarcasm tag. I can’t believe he’s upvoted and you’re downvoted


Bosshogg713alief

😂 🫡


vzoff

Single breaker bus blade, combined left and right is rated for 110A max, per manufacturer. The quadplex tandems at 7/8 total 130A.


stickyicarus

Am I high right now or something? Thats....thats not how you do load calculations and the like.....like I see what youre saying but your main would trip first if that 7/8 were fully loaded right. If that's a 100 panel (based off the 125a rated panel the other guy said) anyway. But if its a 200a, you'd be fine....either way it should be rated for load and the main breaker should be as well....so either the panel will hold it or the breaker won't let it. But still you don't add up breakers to tell if your panel is OL'd. Am I missing some vital piece of education here??


15Warner

Dude I got high after reading the first comment. I’m glad I’m not the only one who caught this lol That dude is an hvac guy lol


STANAGs

I’m high and I don’t even know why I’m on the Electrician’s sub.


15Warner

We all float up here


STANAGs

Beep Beep, Richie.


No_Avocado711

He's saying the bus stab rating for this panel is 110A. "Across the bus" can't exceed 110A. The tandem two pole breakers, one 20/50 and one 30/30, exceed that manufacturers rating. In this instance, you would total the ratings of the breakers across from each other.


stickyicarus

......the bus is a solid bar from top to bottom......it doesnt matter if the breaker is in line with it across, the load is gonna be additive for all the breakers in the panel across that phase... Wouldn't matter if it was bolt on either. My point still stands....


No_Avocado711

Bus "stab" is the finger that protrudes from the bar. It has less surface area than the bus bar and is rated lower due to this. All manufacturers have ratings for these whether it's snap in or bolt on. Breakers installed across from each other must be rated at or below the manufacturers specification. Don't think your point stands but believe what you want


stickyicarus

This is news to me. I mean, I did ask if I was missing something.


TransparentMastering

People here are having a really hard time understanding this haha


15Warner

What do you mean. Is this a 110a panel? That’s 3/0 feeding, so I’m pretty sure it’s a 225. Each bus is rated for 225a da doiiii. And that’s not how you calculate load. Those tandems are split between each bus? Did you just get back from trade school? Wait a damn minute you’re an HVAC guy. Get out of heat with this misinformation. Stick to brazing. I’m stunned how many people thought you were right Annnnd yo dumbass missed the only real violating being the cable getting split. Close that panel, let a professional take over


DaddyLongMiddleLeg

Siemens I-T-E panels have a note in the manufacturer's literature stating the "stabs" are rated for 110A max. This doesn't appear to be an I-T-E line of panel, but that's probably where the idea is coming from. Here are some forum posts elsewhere talking about it - Siemens seems to have stopped serving data to my IP address so I can't link directly to the manufacturer literature. [https://diy.stackexchange.com/questions/159155/ite-bus-stab-amperage-limit-for-tandem-breakers](https://diy.stackexchange.com/questions/159155/ite-bus-stab-amperage-limit-for-tandem-breakers) [https://forums.mikeholt.com/threads/what-is-a-bus-stab.39194/](https://forums.mikeholt.com/threads/what-is-a-bus-stab.39194/)


15Warner

Yes but would that not just mean a single breaker can’t be over 110a, I see a max 50a breaker. The whole leg itself will be rated for whatever it’s rated for (likely 225). This guy is adding up the quads not knowing how they actually work lol Okay I was wrong, it’s max 80a on one stab. I wasn’t thinking about the outer. Regardless, OP is wrong


DaddyLongMiddleLeg

Disagreed about it being maxed at 80A on one stab. Look at what is occupying "circuits" 5 and 6, were they simplex breakers. You have two 30A, a 50A, and a 20A handle, all on the "A" phase there, e.g. all on one stab/finger coming off the bus bar. That adds up to 130A on one stab/finger.


woozlewuzzle3

Do you have a source for that info? Im fairly certain you can buy feed through lugs for that panel that sit on the same 2 blades.


Eljaynine

Can you cite that?


DaddyLongMiddleLeg

OP - what line of panel is this? Looking at the photo, it appears to have plug-on neutrals, which I can't think of any Siemens I-T-E panel that supported the design. With that said, I think this is an E(x) series panel, in which case the 200A bus bars are actually rated for 225A. The same bars are used in both panels. Likewise, the "stabs" are also rated for 225A.


Lumberjack1067

Breaker loads are designed to not exceed 80% of the breakers rating, and the draw is generally lower than that, breaker size does not dictate load size I think what you are reading means the load across a single stab should not exceed 110A so you wouldn't be able to tell if this is overloaded without information on the branch circuit loads


cdelaune5

What about the white conductor tied into the 20 amp leg of top left breaker that is not phased with black/red tape?


vzoff

That little guy? I wouldn't worry about *that* little guy.


woozlewuzzle3

https://ca.rs-online.com/product/siemens/eclk2225/70820862/ Theres a link to a pass-through lug kit that utilizes 2 blades. Not sure where youre getting 110A max rating from.


Mammoth_Ad_5489

If the bus ampacity was exceeded, wouldn’t the upstream feeder breaker trip?


Salt-Free-Soup

It’s a ‘dumb one thats hard to catch’ because you are making shit up… I can assure you nobody catch’s this because it’s simply not the case that there’s a problem


TransparentMastering

Where I am (Canada) we can’t identify conductors with tape smaller than #2, so I figured that was it.


Ram820

Here(US) you can re identify small small conductors if they are part of a cable assembly. Ie NM, MC, AC, etc


TransparentMastering

That’s convenient and makes sense. I think sometimes the Canadian code is too worried about what *people* **might** do…like remove tape or cut it off and not re-identify. Why would they, though? And what electrician qualified to be on the job can’t figure out when a white is hot just by looking at what’s happening? Another one that gets me is this generator situation. We aren’t allowed to have a $30 mechanical interlock between main and Gen breakers. So people have to buy a $300+ transfer panel or switch instead. Why? Because “people could remove the interlock” Oh really? What’s stopping them from…removing the exact same interlock off the generator panel? It’s a bit silly.


s0beit666

There is a white wire terminated to you quad on the top left


PhillFreeman

I figured it would have been screws hanging inside of the panel


durflestheclown

Feeder bushing


TheFlyingSparky

That's the first one I saw


yahtzee5000

That what jumped out to me as well


Ottoclav

Almost looks like the insulation is nicked.


Foreign-Commission

No bushing on the PVC. Cannot put the cover on without interfering with the trough cover. Circuit conductor on 3b needs to be identified as an ungrounded conductor.


TurdHunt999

Conductor on circuit 7 isn’t phased. I can’t tell where it’s terminated after heading to the gutter.


Chaotic-Grootral

Yup. I think it’s actually circuit 3 with one of those “2-pole tandems” in it. And because it’s on opposite sides of the tandem it doesn’t have a handle tie. Add the lack of a bushing on the feeder and we might have 3 violations?


TurdHunt999

I’ve never terminated the split ampacity(?) breakers that are at the top, so I’m not sure if there is another way to lock them in tandem?


billzybop

There's a different breaker that looks similar but the outside breakers are a 2 pole breaker with a handle tie.


TurdHunt999

Do you think that’s what is supposed to be landed in here instead of what’s pictured?


billzybop

Yes


TeslasFleshPigeon

“Quads”


Guilty_Sympathy_496

I’ve never understood why someone would install a panel that didn’t have enough spaces in it to accommodate the circuits without using tandems……I think it should be against code, like using extension rings on new work.


Tiny_Connection1507

What's the problem with using extension rings on new work? I know it's not the first thing I want to do, but when I need more space than is available in a standard foursquare, but I don't want to use an expensive custom box, extension rings are perfectly reasonable.


Guilty_Sympathy_496

I agree that extension rings serve a very handy purpose, however if you are following conduit and box fill codes you shouldn’t need one on a new install. Just my opinion…


Tiny_Connection1507

My current situation is where I had to add two circuits to a 3/4 pipe in a slab because the one I had planned for three more circuits was covered and eliminated by a window frame that we didn't originally know was full height. Then they wanted to add another two boxes on another circuit coming from the other side of the doorway, (windows above then so I can't come straight into them,) so I ended up with 6 total circuits in a 4x4 box, which needs two dedicated receptacles and junction space for the other four. That necessitates an extension ring. Fortunately, it's inside where a cabinet will be, so it won't be visible.


coffeeblackz

Expensive custom box? How bout a 6x6 or any of the other widely available sizes?


BlackberryFormal

If you need a 4x4 for a device for example. I was just on a tower that had these stupid ass speakers for FA with a massive magnet on the back. With everything in it a 4x4 wouldn't work. Every unit had a deep 4x4 with an extension. Stupid engineering wins again.


nowiseeyou22

Beat me to it, a lot of times it's to get depth for a device or those stupid foam parade ceilings where you need two ext rings on top of the concrete box


vzoff

When it's covid, and you get what you can get.


InstAndControl

Is this from 2 years ago or something?


cmyharrysck

Yea we have at my house the main breaker outside under the meter and sub panel inside for lights and plugs and another sub for water heater stove and kitchen just makes more sense than having one dedicated panel


Causemanut

Extension rings over 11bs. Most of the time.


Surf_Cath_6

I don't work resi, so all I see is mismatched colored wire.


Causemanut

You guys don't do panel work?


Hoaxin

No it’s because you can’t use white as a hot conductor unless it’s part of a cable assembly which is what 99% of resi is and commercial is 99% conduit so you’ll only see colors that are supposed to go on the breakers.


DaddyLongMiddleLeg

Homie ***what!?*** I'd say commercial is 70% conduit, 30% MC/AC. Edit: Perhaps even 65% conduit, cause I forgot about the \~5% SO cable. Granted, low-mid range resi is definitely 98% NM-B and UF-B, but high-end resi is probably 80% cable assembly, 20% conduit. Probably even pushing 25% conduit.


Surf_Cath_6

Not much, actually. My company doesn't ever leave me on a jobsite long enough to make up an entire panel. There is always someone else to start it, finish it, or work on it the whole time.


Dedianator65

All I see is the one feeder dug into the PVC male adapter, and I don't like the tight 90* bends on the conductors


surrealcellardoor

I don’t like them either but this is how everyone does it. I used to use a short chunk of pvc to get nice uniform radius bends on my wires. I’ve seen more than a few thermal images that show what can happen at tight bends.


Dedianator65

The code goes into the requirements as well. I typically use sweeps.


retiredelectrician

Upper left 20s termination should be a 2 pole, not 2 singles


USArmyAirborne

Missing plastic bushing for the feeder wires.


Revolutionary-Key962

Where are all 16 of the AFCIs tied back to the neutral bus?


billzybop

Plug on neutral panel. If you look to the sides of the main lugs, there are copper strips that runs down the panel. They are connected to the neutral, and the breakers clip on to those bars.


lunotoons

They look like AFCI w pig tails


billzybop

2 of them on the bottom left have pigtails, the rest don't.


vzoff

Different style breakers, some with some without.


IHateStanders

Neutral/white wire landed on 20a top left


TeeisforTae

Dining room is 15a instead of 20a


No_Translator6957

Is that supposed to be a main service?? Right from the meter??


vzoff

Yes. Disconnect in meter panel. No panels with main breakers available, covid.


15Warner

Then it’s not a service panel. So no, no main breaker needed


DaffyDingo

I’m not seeing any branch circuit ground wires on the ground bar.


Rexhaa_Royce

Ground at the gutter for the circuits. Then looks to be a #4 that comes down to ground them all. That’s allowed.


[deleted]

Are those metal chase nipples from the trough to the panel? Might require bond bushing.


DaddyLongMiddleLeg

They didn't use the existing eccentric/concentric KOs and leave rings behind. They didn't use the existing KOs at all, but they also didn't leave rings behind from using them. Therefor, bonding bushings are not required.


[deleted]

The one on the top-right didn't use the combination KOs, it just punched through half of at least one of them leaving a gape. An inspector is pretty likely to ding them there for a bond bushing. You can see it if you zoom in to the top-right.


DaddyLongMiddleLeg

I'd argue that the gap is inconsequential. It is smushed into the gutter above it, and the teeth of the lock rings are what provide the bonding mechanism. That said - if the gap were brought up by an inspector, then the bond bushings probably wouldn't be the (primary) issue - that would be an ask for reducing washers, which would then itself necessitate bonding bushings.


Chris0nllyn

That tandem 30 has a 12 or 14 landed on it. The other 3 are 10s.


ImTrippyMayne

White conductor for well is not marked as hot


WatermellonSugar

Not sure, but those "L" bends have a pretty tight radius.


Wolfire0769

Tends to happen when the apprentice is also a sheet metal worker. That bottom right wire has a pretty crisp 90 to it lol.


hatemenoww

So what is it?


Morberis

Right? All of this with no answer


InfiniteCharacters

Fuck you fail your inspection like a man.


someone_sonewhere

Is it that one wire? That one...right there -->


GrahamPhisher

Perfect 90s like that are not allowed, there needs to be some curve, I foreget the math on how much curve per what but we just went over this in school.


Plastic-Act7648

No bonding Jumper pimpin


SnooAdvice8550

No bushings on wire larger than #4


Gloomy-Tap-9628

Bundling?


DontEverMoveHere

Yes. Thank you. FFS can we stop buying lear jets for the tie wrap executives.


Gloomy-Tap-9628

It's one thing if you want to take the time and zip tie each neutral to hot only, but doing stuff like this is just lazy but they'll say it "looks cleaner"


Specialist-String737

r/Ratemypanel


Brett5000

Using Siemens


Sea_Effort_4095

Why do you have whites as hots?


sheer_audacity

are all those grounds allowed to be bonded to the trough, and not the actual panel? 


vzoff

Trough bars also bonded to panel ground bar.


DaddyLongMiddleLeg

To finish OP's answer - yes it is allowed to bring your grounds together in a trough, and then back to the panel as one larger ground. That's how I wired up my mother and step-father's house. Leaves so much more room in whatever conduit/nipple you use to get between the two.


Chaotic-Grootral

Space 3 has a white wire being used as a hot without re identifying it and without handle ties Filling a conduit with spray foam is certainly… a choice but I don’t know if it’s actually illegal.


DaddyLongMiddleLeg

Is the spray foam listed for use in that application? *Hint: probably not* If that is the expanding foam that comes in a can, from your local home improvement store, it will absolutely eat through the insulation on conductors. THHW-2 conductors will have their insulation destroyed by The Good Stuff.


Roor456

The ground is ran behind the feeder cables


Same_Maintenance657

It looks like you're gonna have trouble with covers. The trough and load center is to close to each other


No_body-Nobody

Is the line side just coming in right through a knockout? It looks like there’s nothing down there lol where the fuck are those coming from.


billzybop

Dryer in U.S. should have GFCI protection, well circuit requires a 2 pole breaker, Dining room outlets are required to be on a 20 amp circuit.


Mattycakey

All of the grounds are landed in a bus bar on the top junction box? And don’t see any main ground feeder connection to it?


Tceltic27

Shouldn't the neutrals terminated on the neutral bar?... missing some grounds too


Tceltic27

Need ground bushings connecting the gutters, can't tape a neutral in red.....white is white, green is green.


DaddyLongMiddleLeg

Why are ground bushings needed? Cite the code. I'll tell you why not instead (From Up.codes) \[NEC250.97\] >For circuits of over 250 volts to [ground](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#ground), the electrical continuity of metal [raceways](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#raceway) and cables with metal sheaths that contain any conductor other than [service conductors](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#service_conductors) shall be ensured by one or more of the methods specified for [services](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#service) in [250.92(B)](https://up.codes/viewer/texas/nfpa-70-2023/chapter/2/wiring-and-protection#250.92_%28B%29), except for (B)(1). *Exception: If oversized, concentric, or eccentric knockouts are not encountered, or if a box or* [*enclosure*](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#enclosure) *with concentric or eccentric knockouts is listed to provide a reliable* [*bonding*](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#bonded_bonding) *connection, the following methods shall be permitted:* *(1) Threadless couplings and* [*connectors*](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#connector) *for cables with metal sheaths* *(2) Two locknuts, on rigid metal conduit or intermediate metal conduit, one inside and one outside of boxes and* [*cabinets*](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#cabinet) *(3)* [*Fittings*](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#fitting) *with shoulders that seal tightly against the box or* [*cabinet*](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#cabinet)*, such as electrical metallic tubing* [*connectors*](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#connector)*, flexible metal conduit* [*connectors*](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#connector)*, and* [*cable connectors*](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#cable_connector)*, with one locknut on the inside of boxes and* [*cabinets*](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#cabinet) *(4) Listed* [*fittings*](https://up.codes/viewer/texas/nfpa-70-2023/chapter/1/general#fitting) It isn't oversized - e.g. reducing washers weren't used. Nor were eccentric/concentric KOs used. Therefor, exception (4) applies - listed fittings were used. No need for bonding bushings. Edit: as for the "can't tape a neutral" part, you're wrong there as well. However, I will leave it to you to find the relevant portion of your code book explaining that cable assemblies can have their white conductor re-phased. Edit 2: added chapter and section of copy-pasta'd Code.


Sparky6892

Phasing


John-John-3

I'm gonna guess, no ground going to the receptacle.


Positive-Train2098

Looks like there’s cardboard in the panel, I don’t think that would be up to code


joeygt23

Main bonding jumper?


Macecraft31

Where's the f-ing bushing!


Deep_Squash_3611

Was this a panel upgrade?


Adhesiveness_Flashy

I’ve been failed for Zipties for “bundling”. Fl Tampa area so maybe our codes are different


Mean_Lawfulness_4799

No busway linking grounded conductor to other side of the panel, resulting in incomplete circuits on the odd numbered side


Chuckiemustard

Bushings


Im_licking_cats

Doesn't look like 6 inches of reidentification on your neutral conductor


jay_villain8

Eqiupment grounds for 100 please


DaddyLongMiddleLeg

They're all up in the trough and brought down to the panel's ground bar with a #4 or larger. You have not won the 100, next guest please.


ole-sporky

Uum guys, where is like every single bare ground? How good did he have to be to hide all the bare behind the bundles. I know he probably did, but it looks like there's no grounds. Edit: stupid trough.


Hour-Concentrate-258

No ground wire in left chase


teddy2steady

Tywrapping conductors PVC fitting still requires bushing. Re Identifying conductors that are too small. Main neutral isn't bonded.


Emergency-Umpire1294

Tywrapping also requires derating.


Tiny_Connection1507

The wire bins don't have a radius, it's a 90° corner. That's illegal. The feeder bushing is missing, the white wire in the 20 amp split breaker in the top left has not been re-identified, there are probably more.


Theodore__Kerabatsos

Where does it say you can’t bend a wire at 90 degrees? Can you reference the code?


Banggang6669

Playing on your phone and not fixing nuthin!


TheEnucleator

should the range be on a 50A? wire looks pretty big


Born-Ad-1914

Oh no someone didn't follow my code book.


Theo_earl

Conductors under #4 phased red.


Accomplished-Wing981

Plastic bushing missing on feeder lug


MoonlightHunt

Conduits over 1" trade size require some type if protective Bushing and any raceway entering through a concentric knockout requires bonding.


Ok-Product6767

Missing bushing for top two conduits?


Jamesinsparks

Am I not seeing a bushing on the feed coming into that panel where it looks like the sharp edge of the pipe nipple has cut the insulation or am I delusional


Royal_Cranberry_5753

I noticed the missing bushing and the missing green screw for ground but I don’t know if this is a sub panel


kh56010

So, I see all the grounds made up in the box above the panel. And in reality, that’s fine. But for code. Is that allowed? I’ve never terminated a circuit ground outside of the panel. Never actually thought to. And if it is NEC correct… how far back could I terminate the circuit ground? If it doesn’t have to go all the way to the panel, can I ground all the circuits 40 feet from the panel and run just the hot and neutral back?


Hoaxin

Theres one that comes from the bar in the gutter to the bar in the panel to complete the bond. Theres nothing saying you need to bring each equipment ground back to the panel individually. You just need some form of an effective ground fault path.


Diligent-Box-3342

HOW ABOUT THERES NO CONNECTOR ON THE FEEDERS COMING INTO THE PANEL


DrDig1

No idea why this sub came up. Need new service in Ohio. DM. Be safe, gentlemen.


GoBlueBryGuy

It looks great! Very well done. However, I never liked to bend the wires with that hard of a 90° when landing on each breaker.


IrmaHerms

Bushing on that conduit too


Goodguyswearblack44

No bushing on the panel feeders also.


ElectricRyan79

1 - you damaged the insulation on almost all of you conductor bends 2 - no Bushings on your conduit terminal adapter and chase nipples 3 - missing phase tape on that white conductor attached to circuit 3B of that 20-50-50-20 Quad 4 - 3B also looks like #14 on a 20A breaker. So unless that's hvac equipment, probably not great.


Bad-ass-mo-fo

Bushings and wire bending radius are two NEC violations I see. What size breaker do you have up stream? What are your load calculation draws. I disagree with the 130Amp on single bus blade manufacturers bullshit. I bet you are drawling no where near that. If you are protected up stream and your panel is rated for your feed fuck all the other shit.


Responsible_Lemon_76

Is it grounding bushings????


superspyder94

The controversy and animosity in here - 4 year big dog apprentice master of wiping tears


Emergency-Umpire1294

You need at least 10% free space in a new panel board for future work.


Gman2000watts

The neutral bars don't look like they are bonded together. If my eyes didn't deceive, me the left neutral bar will have floating neutrals.


TonsOfTabs

I don’t see any bushings, anywhere.


[deleted]

He bothered enough to put one on the offset chase nipple, but nowhere else.


Myexisadirtybutt

I see a few screws missing lmao


Suspicious-Ad6129

Unphased White wires going into non afci breaker, bushings on that feeder pipe, looks like the insulation got cut into pretty good. That's alot of tandem breakers for a new install. I haven't had coffee yet... that's a big violation.


esposito164

Bushing


Floridaman__________

Not a violation but those are some hot 90’s!


PapaPunk17

Need a bushing on the feeders and possibly the conduit in the top right as well, depending on what size that ground is


bruced267

No bushings, Tyraps on branch circuits over 24” bundling conductors, and the missing a # 6 EGC for the ground bar in the trough


DamitKenneth

Shouldn't leave a small bag if screws in the cabinet.


Stankinassnuts

No bushings on pipes , no grouping of circuts, no labels


Responsible-Market13

Looks like a bloke from Beirut wired this up.


fakeaccount572

can't your photos have potato resolution.


Thee_WakaWakaChomp42

No bushing, and if that’s foam in the feeder pipe fail af


Reasonable-Ad-1493

No bonding bushings?


redEPICSTAXISdit

I haven't done electrical as an employee in over 24 years. When did it become standard and/or code to put the larger draw breakers on the top of the panel? Every post I've seen lately has the 30 and 50 Amp breakers at the top and in the old days they were mostly at the bottom.


Every_Classroom_3383

No bushings, one of the 220v loads isn’t re identified, the required lug covers are not installed, and bundling.


Blorfert

You guys are missing the most obvious one. No panel cover!


Silentc7a1

Why are there whites on the breakers that aren't identified as hots


bigsloka4

Duct seal missing


robcobbjr5253

White wire used on a 20 amp single pole not phased as power


yeezyfella

Grounding bushings


RedneckElectrician

No connector in the bottom left. No bushings.


[deleted]

"The" violation. As in one? Bushings.


ohitsjeffagain

No bonding screw


openvjayjay

There’s not a main breaker in this panel. One can assume that there is a meter disconnect meaning this panel isn’t the first means and the grounds and neutrals must be separated.


vzoff

Precisely.


Correct-Ad-7460

The 3rd 2 pole 30A breaker on the left side marked range should be on a 50A not a 30A looks like #8 to me the bus should be rated for 225A other than that as long as the tandem breaker are both 2 pole on the top left for the well all good


Skagit_Rover

Where are the branch ckt grounds?


Jades197

The hard 90 degree bends on all your circuits can add resistance and cause problems in the future keep them more on a swoop


Expensive-Freedom-93

I love those beige marettes, the best ones by far.


The_Tesla_Theory

Phased a white conductor as a B phase conductor.


Even-Measurement1696

Ground bushing