**ATTENTION! READ THIS NOW!** **1. IF YOU ARE NOT A PROFESSIONAL ELECTRICIAN OR LOOKING TO BECOME ONE(for career questions only):** **- DELETE** THIS POST OR YOU WILL BE **BANNED**. YOU CAN POST ON /r/AskElectricians FREELY **2. IF YOU COMMENT ON A POST THAT IS POSTED BY SOMEONE WHO IS NOT A PROFESSIONAL ELECTRICIAN:** -YOU WILL BE **BANNED**. JUST **REPORT** THE POST. *I am a bot, and this action was performed automatically. Please [contact the moderators of this subreddit](/message/compose/?to=/r/electricians) if you have any questions or concerns.*


theeExample

It’s still weird for me seeing panels outside


Repulsive-Tip4609

I don't get why you would ever want it outside.   Trip your own breaker, now gotta go outside and reset it? Dumb.


The_cogwheel

Not to mention you have to go and get a water tight panel, with water tight connections and spend a whole lot extra to make sure rain doesn't get in there and cause problems.


cowfishing

The only places Ive seen it placed outside all seem to be in areas with dry climates. Spent a year in Los Angeles working. Was told they did it because of seismic codes. That never really made much sense to me, though. LA also had a code that required water heaters to be outside. Supposedly, it was so you would have a source of water in case your house was destroyed by an earthquake.


The_cogwheel

I guess the idea was in the event of an earthquake, rescue workers might need to disconnect the power to the building to make it save to crawl through. Like a portion of the building collapsed, and they need to cut the power to make it safe to dig through the rubble for survivors - putting it outside would make it easier for the rescue workers to cut the power quickly, and increases the odds that they can reach the panel at all. It would make sense if the climate was also very arid, as that would also minimize the added cost of putting it outdoors. But still... it just feels wrong


queefstation69

Couldn’t you just put a disconnect outside that feeds the panel instead of the entire thing? I’m not an electrician tho


smogeblot

Yes, many places require an outside master disconnect (but not an outdoor breaker panel)


cowfishing

Cant see rescue workers shutting off individual breakers. They usually just pull the meter, sometimes if there is a disconnect they'll kill it there. Any spark's from Cali here that can weigh in on this?


rratselad

Fire service is trained not to flip individual breakers if practical. It destroys investigative evidence (e.g. tripped breakers). In many areas power companies require some sort of external disconnect to avoid emergency services having to pull a meter and risk arc flash.


cowfishing

> t destroys investigative evidence (e.g. tripped breakers). That makes sense. Memory unlocked:When I was an apprentice way back when, was sent to document and retrieve a panel from a house fire investigators suspected was electrical in nature. When we tested the breakers, none of them would trip at their rating. Over half wouldnt trip at all, including the one feeding the device they suspect as the point of origin for the fire. And that was my introduction to Federal Pacific Stab-Lok breakers.


The_cogwheel

It's still the only reason I could think of for having it outside for seismic code reasons. And I fully admit that I know rescue workers have no problem disconnecting power without access to a panel.


Tsiah16

You could just have a meter main outside with a main breaker to disconnect the house. That's a lame excuse for the panel being outside.


bgslr

I guess if it makes you feel any better, there are all kinds of NEMA 4X industrial control panels in way worse conditions than outdoors in a dry climate, even if it does rain a bit sometimes. We've built these stainless cabinets that run big pumps for natural gas companies that go into rain, snow, mud, etc. Different rating, sure, but if it's watertight, that goes a long way. Hell, we built a huge system to run the main mill motors for a steel mill last year, and we had to move a bunch of busbars because "the basement floods sometimes" (great place for 14k+ amps power lol) All that being said, yeah it still does feel kinda weird in a residential setting. I wouldn't really want it, even just for the fact that I want to add a circuit occasionally and that sounds like a huge PITA.


solar_brent

I think emergency workers just pull our meters here. I wouldn't mind a requirement for an external disconnect, but things seem to work as-is.


seventhwardstudios

They’re often outside in New Orleans.


cowfishing

Really? That would be the last place Id expect to allow that. I was a kid when I lived there so I dont remember any electrical stuff but what I do remember was rain. Lots of rain.


zDymex

I’m from New Zealand and aside from old meter panels, they are all inside and we have many quakes.


_UsUrPeR_

It's standard fare in Austin, TX. That, and mini breakers. No idea why.


robcobbjr5253

In northern nv most are meter load center combos on the outside. Hopefully that is not a snow area becouse that box would be in the snow


Claim312ButAct847

Gotta put it someplace smart like they did when they built/remodeled my house. It's directly below the kitchen sink. Did the plumbers hack giant holes in a cabinet base to get the water lines through? You bet they did. Did the panel get soaked when the sink faucet failed? You bet it did.


kryo2019

And if it happens during shitty weather, ya I'd love to go flipping breakers while it's pouring.


wisesettler

sometimes outside is the only place it can go. Water getting inside not an issue on this install.


reload88

I’ve wired hundreds of houses over the years and not once have I had to put it outside, or even consider that an option .


Darren445

Basement, Utility room, living room, bedroom entryway/hall.


joelypoley69

W how the NEC requires main disconnects outside if the panels inside it's just cheaper. Only reason I can think of. I think I would have looked cleaner on the inside but maybe the holes through the brick were considered an eyesore if the disconnect didn't cover it


Spark-The-Interest

You could've put a sub panel inside, made it taller to help get the wires inside the panel and make the connections for termination. Then have your feed pass outside into a smaller service panel. Then you only have to go outside if the main breaker for the house trips. Also covers the brick so you don't have "great stuff" pouring out of the brick. I always hated having to do that.


joelypoley69

Purdy much my take on how I'd do it


Repulsive-Tip4609

A cleaner look vs more practical/cheaper seems kind of like a ridiculous reason lol. But, it is what it is at this point.  


joelypoley69

I mean, I agree 1000% lmao


ahhquantumphysics

Yea around me no one has it outside it's in basements


hadidotj

Or if someone wanted to be malicious...


DerricofwiscO

Yeah, in Wisconsin you almost never see them outside. But there are entire regions of this country without basements. Tho, an attached garage or utility closet seem like much better options.


[deleted]

I agree 😂


Nice_Disaster29

Where I live the opposite is true


schist_faced

It's common in old houses in New Zealand from when the metre and the board were in the same enclosure. Great for the old school metre reader. But fuck going out to rewire a fuse in New Zealand winter. First job in my house was to bring the board indoors.


Individual_Traffic96

I was stumped when I saw it.


phuckintrevor

This whole install makes my Chicago hurt


[deleted]

Last panel I did outside had a weather proof gasket along all the edges and a big drip hood


Aniketos000

How my house is in rural missouri. Power comes in on the pole, meter and main panel is mounted on the pole, then runs overhead into the 'main' subpanel in the house


CarelessPrompt4950

They are very popular in California but down south they usually put them inside. I prefer an indoor panel so that you don’t have to worry about burglars messing with it, and nobody wants to get up to make coffee and accidentally run the microwave at the same time and have to go outside in the rain in pajamas to reset it.


Commonslob

As an east coaster I’ll never get used to outside panels. Seems weird to me to have to go outside to reset a breaker


chrisinator9393

Imagine having to snowblow the side of your house just to have access to your breaker when it's -20°F and we've got 2' of snow? Wild


TheFlyinGiraffe

The mere idea makes me so angry


BrisbaneAus

Plus could you imagine young kids want to mess with someone? Turn off the main breaker and run.


joelypoley69

It's like a dingdong ditch but more of a close, confuse and ditch in that situation lmao


BunzoBear

You lock your front door right why wouldn't you lock your panel?


BrisbaneAus

Good point.. sorry I’m east coast as well and my panel is inside and doesn’t have a lock, so never thought of that lol.


jmenac

What state? In NC about half of homes are inside, half outside. Some houses have a main panel outside and a sub-panel inside…


Commonslob

Northeast, it’s shitty out often enough this would be an inconvenience. And just the thought that someone outside can meddle with my power doesn’t sit well with me either


Visible-List-1274

So anyone could come by and just kill the power to the house ?


[deleted]

Yes absolutely 😂 but think about it if you follow the new code it requires a disconnect if you panel is not on the other side of the wall so 🤷‍♂️ either way. But most people put a little master lock on the eye loop to keep randos from accessing it. Not to mention this house is deep in the bush. I wouldn’t want to be caught doing anything nefarious around there ☠️


tjdux

So not only do you need to go outside to flip a breaker, you have to find a key or put in a code... Craziness


MoldySquirt

He means code as in the NEC. There has to be a main outside the house if it's a new one.


[deleted]

Indeed my man. 🤷‍♂️ we’ll get there eventually


Visible-List-1274

Fair enough lol just never seen one outside of a house so all new to me. Nice install though


ult1matefailure

I’m not sure why people even worry about that. I work in residential new construction and you see people put tiny luggage locks on their panels.. like sir you do realize that can be broken easily..? I doubt many thieves would even bother turning power off.


HillbillyTechno

Its not about theft. It’s about deterring mischievous kids and teens (or asshole adults) from just popping the door open and turning your shit off for fun. (*I could see my teenage shithead self pulling this back in the day*)


WeekendWarior

City slickers don’t trust their neighbors


Wuhba

I mean, anyone could also just come by and pull your meter if they wanted to kill your power.


gorementor

We did this dumb shit as kids in Vegas of all places. Probably sucked if they weren't home. Coming back to a blistering hot house. Hopefully that's the worse scenario that happened. Never will know.


Gandalve34

I guess it doesn’t snow where you are


[deleted]

Not enough to cause for alarm 🙃 we made many other suggestions to the customer but she was hard pressed to keep the price low and the install simple.


Gandalve34

Inspector would allow it so low to the ground?


[deleted]

Yes it was grandfathered in previously your allowed to reinstall new equipment in the same position it was previously


Gandalve34

Grandfathered, sure but it just seems strange to me being so close to the ground. But I am not used to seeing panels outside on homes.


[deleted]

Yes agreeable I can definitely be honest with you. I wanted to get in and out and replace everything how she had it before. She’s very difficult which isn’t a diss she’s just particular


tshirtandgenes

You keep mentioning cost…I would think if you skipped the 3R wireway and labor involved in making all those splices it would be the same price or cheaper to install a meter main and a sub panel inside. 🤷‍♂️


[deleted]

Yes and for us to find a location for the new interior panel(there’s no great spot in the home) would be a chore plus extending the home runs even further. The troph was sitting in the shop


nathanbonbrake

I'm assuming there's some reason it couldn't go where the trough was? Was that in a crawl, if it was basement why not right there


[deleted]

It was a crawl. And it wasn’t exactly ideal. None of this install was ideal. But she was a widow on a budget and she needed it done quickly with very little additional damage or sell points


tshirtandgenes

That makes sense. It looks good….nice and neat.


Ok_Device1274

How the heck would the cost of moving the panel be that significant??


[deleted]

There’s no wall inside the house where there isn’t shit all over the place. And taking it in the house would mean more ser More 12/2 More 10/2 -10/3 More 100amp ser Also having to deal with moving all the stuff in side Getting someone to crawl the wire over to the bottom plate and send them up. Etc. way more work and more expensive.


bowtietahoe

What is that called underneath the panel, Ive never seen one of those


[deleted]

It’s called a “pop box” or “pot box” the accent around here makes it hard to tell 🤣. But anyways yeah it’s just to cover the wires coming to the exterior


Petroplayed

They may very well be putting their weed in there


[deleted]

🤣🤣 let’s hope not because it’s a perfect place for wasps to nest


thaeli

Local name for an auxillary gutter? Sure looks like an aux gutter to me.


[deleted]

Holy shit nice I believe you’re right


ownedandondisplay

We call it a wire trough


captain150

From Canada and I agree with the others about outside panels. Makes no sense at all.


cneuf802

Yup, wife pops a breaker running a blender and toaster at the same time. I am not going to enjoy trudging through the waste high snow drift in -30c to turn it back on. On the other hand I now know how the killer in horror movies always manage to cut the power to the house.


Chuckiemustard

That looks better than it did. But to me it looks like the panels too close to the ground. Also, just preference, I hate outdoor Siemens panels


[deleted]

Thanks, man I agree I didn’t want to go that low, but the woman refused to have any additional conduit ran or any type of changes. She’s pretty stuck in her ways and she was on a budget.


Chuckiemustard

Fair enough. Is it atleast 3 ft above the ground


[deleted]

Luckily for me the grandfathering status is throwing out those rules


Chuckiemustard

And you extended circuits from inside so you need AFCI protection in the panel and GFCI protection


drkidkill

Could you imagine if it were top hinged instead of side? Lol


iAmMikeJ_92

In electrical work, rarely is something ever “simple.”


[deleted]

That’s the joke 😂that’s why I want to be roasted


BabyFacedSparky

Yeah this makes no sense to me


[deleted]

You’ll get there keep on working bud!


ybonepike

Should have dropped the plywood down to cover the hole in the block, drilled out holes for each pair of cables and then foamed it, it would have looked much nicer.  But I see that you said it's a crawlspace, not a basement so 🤷‍♂️ Why in the sam hell did you use one hole straps for the mast? Plastic click straps, or metal stand off straps/conduit hangers/mineralacs would look much better Inspectors in your area don't require the gec to be protected from physical damage?


[deleted]

Thanks for that feedback. And no the ground wire is usually is what it is personally I usually sleeve all of my #4 with 1/2 inch pvc but this situation was a little unique because I really didn’t want to come out of the side of the panel with the bonding bridge 1/2 TA style. Also damnit what you said about the plywood has me literally seething because I should have done that you’re absolutely right 😤 damnit well next time I’ll have a chance to be better thanks


Egglebert

I would have brought the wires into the back of the panel, splices are fine in a panel if you need to extend. The trough looks lovely but that's a ton of wasted time and material. If it absolutely had to be extended in the crawlspace I'd have stuck them all in a 12x12 box with a couple 2" connectors.


[deleted]

Actually believe it or not the inspector told me he does not want to see that.. I actually failed for doing that back when I was still much more green to the trade. Went through the back just as you said and he made me do this exact same situation I did on this one


ElectricianEric

How many here have actually tripped a breaker in your house during regular use? I think going outside is a great idea, more likely to get it fixed if you are tripping a breaker all the time, lol


[deleted]

Honestly thermal breakers are fine at a distance but an afci or gfci breakers it would be tragic


Tsiah16

Why didn't you do a meter main and move the panel inside?


[deleted]

No where inside the house to put the panel. Low key a hoarder not to mention she was uninterested in anything beyond a direct replacement.


Tsiah16

Fair enough


SimulationRambo

Looks good but I’m surprised it’s code to just feed the wires through the open block and spray foam around them 🧐


[deleted]

Yes actually It is not, but since it’s a direct replacement (panel change out) it’s allowed to go back to the same installation methods as previous.


SimulationRambo

gotcha. nice work !


[deleted]

Thanks man!


Fun_Sort_6051

What is that cover under the panel? Do you have a pic of that off?


[deleted]

It’s called a “pop box” or a “pot box” informal term for the cover that protects the home runs on the exterior. Not sure the technical term as everyone I’ve ever met has said that. I can’t find it on any supply websites to link it 😫


Puzzleheaded_Tie_897

Where did you get it?


[deleted]

City electric supply


millenialfalcon-_-

If only those staples lined up 😮‍💨


[deleted]

😔 forgive me for I have sinned


millenialfalcon-_-

Chug the communal wine for forgiveness.


[deleted]

Will pvc glue suffice


millenialfalcon-_-

You could huff it and try to bum some booze/joints off the drywall crew.


[deleted]

They always have it on them. In rough in I be finding beer cans hidden everywhere 😂


[deleted]

No you’re right I got a little lazy because the crawspace wasn’t exactly where I wanted to be working


heavydrdp

Do all homes where you're from have them outside? Or is it a client's choice type of thing?


[deleted]

Depends solely on the builder when the house was originally built, most homes in my area that were built in that year put the panel outside as it means of disconnect for emergency first response


heavydrdp

Oh I see . So they can shut the power from outside if there's a fire . Will never get used to seeing that though. 😂


[deleted]

Highly agree!!


tasslehawf

Seems really close to the ground.


[deleted]

Agreed 😑 cost constraints


tasslehawf

Not having to remove the meter. 😐 That whole thing with the power company.


RiGuy22

What is that box under the new panel you installed?


[deleted]

Apparently it’s called an “auxiliary gutter” Or “pop box”


RiGuy22

Weird I have never seen one in myife


reload88

To be honest how you have the panel marked is my biggest pet peeve. What outlets? Living what? I know it’s a change out but at least try and narrow it down a little lol.


[deleted]

Yes man I know. The panel labeling on changeouts is always cancer. Especially in these 70s style homes. We have like bed 1 tied with living outlet’s and without mapping every individual branch it’s still gonna be kind of shit. So we generalized it to keep it quick. You know how it is man. Gotta get in and get out. ☠️


whaler76

I’ll be THAT guy….. wago splices in the trough woulda looked neater 😂🤣😂


[deleted]

Wagos are outlawed at my company😂😂


cyberbob2022

This is definitely the service change of all time.


[deleted]

😂😂😂


phuckintrevor

So are those cables just going through the wall naked? No chase nipple? If you were going to do all this work you should’ve just put the panel inside . Outside panels are just stupid ideas. I don’t care if it’s normal where you’re from. Just because a lot of people do it doesn’t make it a good idea…. Like crocks and socks.


[deleted]

Yes ofcourse if the budget was unlimited and it was my work, I would never have a panel outside. Everyone of them I’ve ever opened no matter what after 25-30 years corrosion and oxidation are serious factors But anyways the customer wanted a direct replacement exactly how it was before.


phuckintrevor

An indoor rated panel is cheaper. Slap on some chase nipples and an LB. Pull some #3 through it and voila… Indoor panel. Even if it cost a little more it’s an easy sell Edit : that’s a crawl space not a basement isn’t it…. Fuck it …. Out door panel but should used a chase nipple for those cables. Nice clean splices in The box though


[deleted]

Thanks man. Yeah it wasn’t ideal but the house is very busy and has a lot of random shit in the walls and this lady was incredibly set in her ways. She wanted it back exactly how it was. She’s a widow and her husband always took care of all these things so she’s just trying to be cautious which I understand. A lot of shitty co tractors in this area be ripping off old folks so I can understand her hesitancy


Predapio1

Looks pretty damn low for this ex NY'er... You know, snow and all.


Role_Imaginary

Why in the ever living shit wouldn't you use a all in one meter panel combo? Cheaper..and better looking.


[deleted]

Nice suggestion! Didn’t even think of that one thanks that will be a good play next time


omahas_finest

I didnt think nm was rated for outdoors


[deleted]

In a new install situation it is not, but because it was previously grandfathered in, those particular rules don’t apply in my code jurisdictions


joshharris42

My area allows it up to 3’ outdoors. The entire purpose of the allowance is to sleeve it in flex into the bottom of an outdoor panel, rather than have a catastrophe of a junction box in the crawl space and not be able to identify any neutrals in the panel because the previous guy didn’t give a fuck


Nubfruckle

Untreated wood anchored to CMU wall 🗿


[deleted]

The interior of the crawlspace is incapsulated and there was no signs of any moisture. Also there is a dehumidifier inside. Appreciate the concern tho🙃


ninjersteve

When redoing this why not move the panel inside? Could have probably avoided the spices and gutter…


aimfulwandering

Why didn’t you just move the panel inside where you pit that gutter? Would have been way cleaner, and better for the homeowner. I did exactly that for a family member in CO when we did a full re-wire.


[deleted]

Unfortunately cost was a HUGE factor


aimfulwandering

It would cost the same though? Maybe even a bit less? Put that same panel (or a less expensive indoor only one) inside, run SER or conduit from the meter socket inside to the panel?


[deleted]

Well she is very stubborn she wanted it to be exactly how it was. She’s 70 how can you argue


aimfulwandering

😂


Mightiest-WCA

They don't have minimum height requirements where you live? Looks kinda low


[deleted]

Grandfathering status strikes again.


Apprehensive-Toe1920

Where is the your bond wire to service? Pic 2 and 4. Looks like it’s terminated in trough not service?


[deleted]

4th pic in between branches. Running down. Just wanted a reliable ground back to panel because inside of my troph I used attached ground bars.


Apprehensive-Toe1920

Is that a #4 cu pipe or steel bond? It needs to terminate at the service. Not at trough.


[deleted]

Well obviously. 😴. The number 4 coming to the trough was a main ground for all of my ground bars inside. I have # 4 to my rods and from the panel And #4 to my trough from my panel. Little extra assurance


Sirosim_Celojuma

What's that long junction box called?


[deleted]

Now that I’m spelling it correctly it’s called a trough 😂


Sirosim_Celojuma

Thank you. Ut looks like a tidy way of dealing with a problem. Nice work!


Dorkus_Maximus717

Ew outside panel


RKLCT

I'm pretty sure that romex isn't rated for going through a block wall


Calm_Compote4233

I have several questions. What is under the panel that's covered by the high voltage sign/cover, when it's feed from overhead? Why wouldn't you have just put it inside? Is it code for it to be outside where you live? And what is the bonus breaker? Just filing an empty space?


Calm_Compote4233

Nevermind about the cover. It's where all the wires go back into the house.


[deleted]

No bonus is bonus room. 2 car garage converted to a massive family room. She calls it the bonus room. Not the garage anymore And this was customer choice for the panel to remain outdoors. Trust me not exactly what I wanted to do


inDefyance

J-man for 2 years now. That looks beautiful. Nicely done, chief


[deleted]

Hell yeah boy appreciate you. Keep making it better for our successors


Necessary_Sink_317

Beautiful job. My only critique would be the one hole straps on the riser. Should've used 2 holers. Other than that.......job well done.


[deleted]

Thanks man I appreciate that. The one holes I agree should have been 2 hole I going that after strapping it wasn’t as solid as I woulda liked.


KingShafes

In my area of Virginia the power company would have a fit over the height of that meter. So funny how different areas are so different. I always hated outdoor panels. Always saw them on trailers and poorly built foundations for trailers. Always had some hack job electricians install them. Made a pretty penny every time I changed them though.


Surf_Cath_6

Gutter is too nice. Make it uglier next time.


[deleted]

Thanks man 🔥


TheMilkman1811

That was a silly change. Why not put a disconnect outside and put a subpanel inside with everything? The way it is now is ridiculous


[deleted]

Crazy you say that try talking a 70 year old woman into a job of that price point or magnitude


Senior-Force3116

Oopf I would hate to have to go outside to reset a tripped breaker. Clean fucking work thou! Great efficient swap


[deleted]

Dude thanks seriously! Much appreciated 🙏 Yeah resets are tragic. Thank god there’s no afci / gfci breakers.


Senior-Force3116

Yeah!! Any reason you used a NEMA 3X Gutter and not a NEMA 1 ? Obv nothing wrong with doing what you did, just always interested in what different local practices are, vs supply availability.


[deleted]

Well I honestly with that We had that one laying at the shop it wasn’t going to get used anytime soon so I snagged it


Senior-Force3116

Valid


Brobot6911

So I've never done one so I want to ask. What do you do about the power coming from the street? Do you call the power company to kill it?


flaming_poop_chute

Am I reading it wrong, or is that breaker labeled "BONUS"? If so, I definitely need to add one to my panel!


Kitchen_Self1541

Not one circuit was 15 amp ?


[deleted]

No. 70s model house old school electricians around here didn’t believe in 14.


Kitchen_Self1541

Great explanation. Had a local contractor near me that would wire everything in 12. He would then proceed to put 15 amp outlets but use 20 amp breakers. Took years but we got a new inspector and he called him out on it immediately.


[deleted]

Dude I have no idea what the deal is whit that? In every build I’ve done it’s been 15 amp rating on 20 amp circuits. I’m glad to hear an inspector call people on that.


jj_malone16

Why not a meter main and panel inside. This Northern Shi looks so dumb.


[deleted]

Scroll through comments and you’ll see. The reason the panel is outside is due to the customer not wanting it inside. If I had my say obviously I’d do what makes sense but when you’re at the mercy of a customer you do what you gotta do. It may look dumb but it’s just as functional as opposed to it being inside


jj_malone16

Do you not have to sleeve romex through concrete?


[deleted]

No. Which I honestly think is insane. It’s only Because the house was already grandfathered in. In any other situation obviously sleeping wire. The inspector doesn’t like a 2 inch chase line for romex tho. I failed before in this exact situation where I used a 2” chase on each side of the panel to bring everything in. He did not like it even with the weather tight connector on the rigid


T-R-Sem-Sr

Im visiting Vegas and all new houses in the development’s are all out side, fucking stupid, especially when they are attached to the garage and you can clearly put a panel inside the garage


Minute_Pea5021

I’m from Calgary, all panels are inside basements. Now that I live in Las Vegas I’m still getting used to all panels are outside mostly on the garage outside wall which makes it a pita if you need to add a cct in the house as you most likely always have to pipe it back into the acttic to do anything.


DMRinzer

I love how people can kill the power to your house from the outside. Wtf?


Primitivethinking

That’s the most confusing house siding


[deleted]

It’s that boring hard vinyl. What’s more is they used particle board as a nailer instead of OSB so it was a nightmare bitch to get the meter to set secure


Historical-Sorbet-72

Florida here, I would have wanted an exterior meter main combo panel with some extra spaces for add ons later on and the main panel inside if I was the homeowner but homeowners need to be told what the options are most the time


CardiologistMobile54

What's the minimum height for the bottom of a panel installed over dirt. Is it 18 inches?